switched fcu in shower room.

my mistake. read OP wrongly. if it's outside zone 2 you're OK.
 
Just come across this thread. As long as the FCU is outside zones, ie. 600mm or more from the edge of a shower tray or bath then of course it is allowed.
 
IMO Common sence should take overe the regs IE Shouldnt be fitted due to 1 spray from shower 2 wet hands "forgetting" they are wet 3 CHILDREN
 
Of course common sense plays a part in any design. I have one in my shower room for a wall mounted fan heater. It is mounted outside zones plus about 2m high so no way children can get to it. I agree that we shouldn't just blindly follow regs though, that is why we train and study for years.
 
What about external influences? (steam moisture etc)

Is there anything in this section which would apply to a bathroom outside zone 2?
 
Potential of wet hands, condensation etc, sounds very similar to a kitchen IMO. Are we going to say that 230v plate accessories are not allowed in kitchens?
NICEIC pocket notes 2 has a table of items allowed in the different bathroom zones, outside the zones 230v plate accessories are allowed. Checked with the tech helpline and they have no problem with FSU's and even light switches installed outside of the zones. Obviously don't just go ahead and install without any thought, but in principal there would appear to be no problem.
 
The OP asked if was allowed. Bottom line, yes you are allowed an SFCU 600mm away from a bath or shower if you so choose. Not a grey area at all. Many electricians however, choose not to, and that is their professional decision.
 
I've seen many switched FCU's above 2.25m for bathroom heaters.. I still think this should only be aloud outside zone 2, although 2.25m is outside zones it's still a stupid place to put a switch to the side of a shower..
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
palace dave,
Last reply from
TPES,
Replies
26
Views
4,469

Advert

Back
Top