Switched fuse on meter tails ? | on ElectriciansForums

Discuss Switched fuse on meter tails ? in the Australia area at ElectriciansForums.net

Joined
Feb 7, 2009
Messages
360
Reaction score
16
Location
.
I have a consumer unit change which also means relocating the unit approx 16m away from original position where meter is.
I have (as i always do) arranged for YEDL to come and fit an isolation switch first.
Once this is done the new meter tails will go from the switch under the floor for approx 15m and back up to new position.

My questions are -

1. Do i need to use any form of protection for the meter tails uder the floor or just clip to the underside of the joists?

2. Do I still need to fit a switched fuse after the isolation switch?
 
Last edited:
Meter tails max 3m away with no Switch fuse. So your 16m would need a switch fuse.
So your setup would be Meter - Isolator - Switch Fuse - Tails - C.U

Not sure how you would need to protect tho. Also would you need to RCD protect after the Isolator to the C.U ?
 
I have a consumer unit change which also means relocating the unit approx 16m away from original position where meter is.
I have (as i always do) arranged for YEDL to come and fit an isolation switch first.
Once this is done the new meter tails will go from the switch under the floor for approx 15m and back up to new position.

My questions are -

1. Do i need to use any form of protection for the meter tails uder the floor or just clip to the underside of the joists?

2. Do I still need to fit a switched fuse after the isolation switch?

In answer to your questions;

1. If you are installing Meter Tails then the will be BS6004, Double Insulated just like a Twin and Earth. Both Live, Neutral and Earth should be kept together along the route.

2.Using the above method will require a RCD and Over Current Protection after the DNO Isolator.

If you were to install a SWA then no RCD would be required, just Over Current Protection.

Would be interested to know how much DNO charges for fitting the switch.:)
 
DNO doesn't fit the switch in my area, its the Meter Operator working on behalf of the Energy Supplier.
Cost usually 45-65 pounds. Which is a very fair price.

In this case a switch fuse will be required, wylex make them. Use metal clad for SWA or insulated for tails.

Disagree about the RCD protection, unless the cables are concealed in a wall (assuming TN system).
 
Thanks all.
Thought switch fuse would be needed so just making sure.
Had planned to use mem/kmf switched fuse. Anyone got any advice on better or easier product.
For the sake of making sure, RCD switched fuse would be ok even though tails will be clipped under floor. Anyone able to suggest best option for that.

The meter, Isolator switch and switched fuse will all need to be concealed in a cupboard in what will become a bedroom, least obtrusive options preferred.

Will avoid working with 25mm SWA if possible as long as safety not compromised.

Normal cost for Isolation switch usually 45 to 75 pounds. I would always recommend that route as it keeps everything safe and legal and avoids messing with any pulling of fuses etc. Small price to pay.
I may also add that on many occasions the fuse has been fitted free (not sure if intentional or if they just forget to invoice)
 
What about discrimination,if you are usuing a rcd to protect the mains do you use a time delayed one ?otherwise it might trip before any rcbo/rcd fitted in the consumer unit does.
 
What about discrimination,if you are usuing a rcd to protect the mains do you use a time delayed one ?otherwise it might trip before any rcbo/rcd fitted in the consumer unit does.

You have just given a good reason for sticking with swa surface clipped from the switch fuse to the consumer unit. The switchfuse will give overcurrent protection for your swa. And no rcd discrimination problems between in line rcd's because your rcd protection starts from the consumer unit and not your sub main feed.
 
You have just given a good reason for sticking with swa surface clipped from the switch fuse to the consumer unit. The switchfuse will give overcurrent protection for your swa. And no rcd discrimination problems between in line rcd's because your rcd protection starts from the consumer unit and not your sub main feed.

Looks like its all down to -
a) work with 25mm SWA (3 core I assume for line, neutral and earth)
or
b) 25mm tails from time delay RCD switch fuse.
:confused:????
 
As you are installing a switchfuse between the cut-out and the DB, your outgoing tails can be 6mm if you like, providing you use the correct size fuse for 6mm.;)

Obviously we dont do that and 16mm or 25mm is the norm. If you're using a 60A fuse then 16mm tails are fine, 80A or 100A then 25mm.
 

Reply to Switched fuse on meter tails ? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
328
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
307
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
367

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
667
  • Question
I think it's more towards what the future brings with them and their ability to measure true power. Half remember a video from bigclivedotcom that...
Replies
14
Views
994

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top