This question is purely out of interest, I'm a substation apprentice while we do some LV installation work its not much and no design work fitting only.

But today I've been helping a sparkie friend do some work(just attaching conduit to wall no actually wiring) for local community group.

So the question why is the neutral to the DB from a switched fuse isolated (if that the right term) not switched but at the DB it's self does switch neutrals?
 
Generally neither a switch fuse nor a DB will have switching of the neutral in a TP installation unless it is is a non TN system or a special type of installation.

Most TP DBs will have a triple pole main switch with a test/disconnect link for the neutral which requires the use of a tool.
 
Could be I'm mistaken, I'm a substation apprentice so not my area of expertise.

Would there be anything wrong with having the neutral switched, should also mention it's 3 phase board?
 
Could be I'm mistaken, I'm a substation apprentice so not my area of expertise.

Would there be anything wrong with having the neutral switched, should also mention it's 3 phase board?
Nothing wrong there as long as the nutral was switched along side the line in I.e. Double pole switch.
However isolating the neutral independant of the live a no no.
 
Would there be anything wrong with having the neutral switched, should also mention it's 3 phase board?


If the neutral is to be switched then it should ideally be by a last break/first make contact to prevent the lives being connected before the neutral.
If the neutral contact of the switch were to fail for any reason you could end up with the installation having a floating neutral which can be dangerous.

In an installation where the neutral is reliably connected to earth (TN system) there is no need to isolate the neutral and so the risk of a failed switch contact can be avoided by nit switching the neutral.

In other installations where the neutral can have a voltage between it and earth it needs to be isolated to achy eve a proper isolation and so it must be switched.
 

Reply to Switched Neutrals or not in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

All good thanks, still trying to retire but still finding myself busy as ever. Hope you're well.
Replies
13
Views
1K
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
662

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top