albi

-
Joined
Feb 11, 2009
Messages
124
Reaction score
7
Location
north east england
Any thoughts on SY cable glands for earthing the screen. On a job where a contractor has used stuffing glands at both ends. Cable feed from a 3 phase DB, cable is ran on top of a wall 8 ft up from floor level, then on to try to a 240v switch socket cable is 3 core 4mm
 
You should earth one end of the cable. whichever end is easiest disconnect and remove from the gland, cut back the plastic outer PVC sheaf exposing the frayed installation. Untangle about a 4mm CSA length, the length is dependant on where you can connect to an earth. Twist it together, a drill is great for this, until you have what is a condutor. Cut the rest of the frayed protection off. Try and slide a little of the outer PVC insulation back over your "conductor" and wrap a small amount of Yellow'Green tape to stop the PVC slipping.

Back into the gland, sleeve with Yellow/green and terminate into the earth, and all this is of course you have slack
 
I personally think the CXT glands for SY are the pits!!!

You cant fix the body of the gland to the enclosure beforehand as the braids also have to be tightened in with the washers and locknut. Awful things IMO but I do use them.
 
yep
i assume that the screen has been cut at the gland...
and its not the earth.......
if so it just needs an earth at one end...any end...a bonding clamp on the stripped end would do..
as long as its not in an outdoor situ ...
 

Reply to sy cable glands in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Sounds more positive.
Replies
8
Views
644
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top