D

dogwind

Hi i am after some help please, i am looking at a fluke schedule of inspection and circuit details/ test results, and in the box called system characteristics it asks for fault level(s), its on a TNCS and i have looked in my on site guide and my regs book for the information, could someone please point me in the right direction.
thanks for any help
Regards Ady
 
Oh right thanks, i measured a loop test Ze of 0.39 so do i just devide that into 100Amps as in my main fuse or am i heading the wrong way with this, cheers
 
If the Ze was .39 then you need to contact the DNO as this is too high. It should be a maximum of .35.

Your PFC is measured. It will be recorded as the highest of the PEFC and PSCC.

However, on a TNCS system, they should be around the same.
 
Yes i did see it was high, i am going back tomorrow and will measure it again, the house is empty at the moment. Thanks for your help.
 
Oh right thanks, i measured a loop test Ze of 0.39 so do i just devide that into 100Amps as in my main fuse or am i heading the wrong way with this, cheers

No - you would divide your supply voltage by your Ze. In your case your fault current would theoretically be 589.7amps (230V/.39) which you would record as 0.589kA. In reality your supply voltage will not be spot on 230 so if your meter is working it out you will probs get a higher reading for the pfc. However as Jason said if you are testing it at the main incomer and not a subboard (which would not be classed as Ze anyway) then your value of .39 ohms for a tn-c-s is not acceptable. Are you sure it is a tn-c-s and not a tn-s?
 
Hi thanks for your advice, it is deffo a tncs system and when i re tested i got a lower reading than 0.35 also i realised i hadnt deducted my test lead resistance the first time i tested, i did my 2391 around 7 years ago and unfortunately the company i worked for i didnt get to do much testing so i am a bit rusty, i am self employed and looking at joining NAPIT or NICEIC (bloody part P) so i am trying to get back up to speed, i was also looking at the fault current characteristics graphs in the regs book for mcb/rcbos and unless i am missing something really obvious i couldnt see a time for as an example a type b mcb 6A what time would it disconnect at say 400Amps, i see in the box on the right it says 0.1 to 5 seconds, i wanted the disconnection time to work out a cpc size calculation, the graphs for the fuses seems much clearer for their time/current disconnection times. Thanks again,
Regards Ady
 
Last edited by a moderator:
Hi thanks for your advice, it is deffo a tncs system and when i re tested i got a lower reading than 0.35 also i realised i hadnt deducted my test lead resistance the first time i tested, i did my 2391 around 7 years ago and unfortunately the company i worked for i didnt get to do much testing so i am a bit rusty, i am self employed and looking at joining NAPIT or NICEIC (bloody part P) so i am trying to get back up to speed, i was also looking at the fault current characteristics graphs in the regs book for mcb/rcbos and unless i am missing something really obvious i couldnt see a time for as an example a type b mcb 6A what time would it disconnect at say 400Amps, i see in the box on the right it says 0.1 to 5 seconds, i wanted the disconnection time to work out a cpc size calculation, the graphs for the fuses seems much clearer for their time/current disconnection times. Thanks again,
Regards Ady

400 amps is well to the right of all parts of the 6A line so the disconnection time is < 0.1 seconds or 0.1 for your calculation. As i understand it, for the 6A line it would only be with a fault current of less than 30 amps that you would be concerned that disconnection times would not be met so once the pfc is above that figure you can take 0.1s for your cpc calcs. But it is a good point - when you are putting a time in the adiabatic equation which time do you use 0.1 or 5! When i was at college we were always shown to use the most advantageous one ie the 0.1 s time
 
Thanks again, i did think it would be the 0.1 but i also tried the calc with 5 secs to be on the safe side, as i wasnt sure if i was reading the graph correctly i thought i would ask on here,i still cant see on the graph any that disconnect at 5 seconds so i dont understand why they say 0.1 to 5 it just seems confusing for no reason and it would be easy to make a mistake
Your help is much appreciated
Thank you
 
Last edited by a moderator:

Reply to system characteristics TNCS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

Thanks I re tested this morning as I had other bits to finish off . I tested three times and it was 0.30 every time . It may have been my leads...
Replies
7
Views
2K
Concerning isn't it. I fear it's just going to lead to reduction in standards and entry requirements and flood the industry with even more poor...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top