Table saw motor wiring | on ElectriciansForums
Discuss Table saw motor wiring in the UK Electrical Forum area at ElectriciansForums.net
P
polaroid
Hello people. My old man has a table saw and water has got in the switch, he decided to remove it ready for me to replace and due to poor memory can't remember how it was wired up.
I've not had much experience with motors etc but from what I can work out it's wired as follows:
[ElectriciansForums.net] Table saw motor wiring
I haven't checked the windings but these are the connections - the nice bright white cables are the capacitor:
I've got a new NVR switch so I assume it's N = 0v and BR & BL = 230v?
From what I see online it's an unusual setup as most single phase motors only have two windings with a capacitor shifting the phase for the second winding.
Cheers!
Can you give more info about the motor? Is there a wiring schematic under the electrical cover? Can you post a photo of the info plate on the motor?
I had a good look around it and the only other bit of info is the plate on the actual table (forgot to upload this initally). The motor plate must be concealed and would involve taking most of the underside apart. I can do it if needed but it's 100 miles away at the moment.
The motor wiring looks like a star Y connected Steinmetz connection to run a 3 phase motor from a single phase supply. Is the capacitor about 140uF? Ie 70uF for each kW of rated motor power. The motor power is 2kW.
JS-Technik GmbH - https://www.js-technik.de/en/faq/detail/groupid/4/id/75
I would carefully label and record the ends of the wires in the terminal block and using a
multimeter set to low Ohms confirm the windings are connected star or delta and how the capacitor and power leads are connected to the motor coils. Note well that even if two wires to a coil are the same colour they must be connected back without introducing a swap over.
If you draw this out and post it folk will check it for you.
The motor used is I reckon a typical star wired one, wound with coils to operate from a standard three wire 400V line to line supply - so 230V across each coil in star configuration. To achieve the same winding voltage from a single phase 230V supply the star point is connected to neutral and two of the three coils to the 230V line. Steinmetz capacitor connection creates a phase shifted line supply for the third winding. A 230V line and N connection across two coils would reduce the winding voltage to 115V reducing motor power considerably.
OK... Below is the motor plate and a wiring diagram. All connections were broken down and measurements made accross the windings with a MFT. I double checked it all as the resistances were not what I was expecting - values come out the same the second time around. The 3 windings resistances were 0.14, 2.1 and 6.7 ohms. The 3 core cable is the feed up to the switch. I'm guessing the difference in the winding resistances are not good.
Many thanks for the help.
The motor is single phase so what I mentioned about Steinmetz does not apply. I do not have time to think on what you have reported - big football game tonight - but I want to say that I would not be surprised if that motor has overheated and suffered internal thermal damage since the exterior cooling fins have been filled with sawdust and chippings which will act as superb thermal insulation blanket and hamper cooling by this surface construct.
Reply to Table saw motor wiring in the UK Electrical Forum area at ElectriciansForums.net
I would agree that the motor is by far the best part to replace. if it is powered and not turning then it is broken. Keep it simple!
If you want to use the motor, you will need to get that thermal cutout working properly, and be certain it does! The little phosphor bronze...
  • -NikD-
  • Ireland
  • 18
  • 1K
