I have a ring cct (2.5mm ) in my cabin which is protected by a 20amp RCBO. This has been in existence for over 3 years with no issues. I recently bought a table saw and when turned on, on its own all is OK. However the other day I had a heater and a dust extractor on, then turned on the table saw, the RCBO immediately tripped. It only trips when other appliances are on and you turn on the table saw. My question, is there a way to dampen the start up of the tablesaw motor or would I have to upgrade the RCBO to 32amp. The table saw is a Dewalt with a 2000watt motor. It is a bit aggressive on star up. Ideally is there something it can be plugged into to reduce the initial surge it creates.
 
The simplest solution is probably turn the heater off while sawing!

As the others have said, you are likely pushing the circuit design as heating generally consumes a lot of power. I'd expect if you look at the ratings on the extractor and the heater and add up the power in watts, and then add 2000 for the saw you'll be at over 4600 watts which in simple terms is the peak limit of a 20A circuit, and it shouldn't be running with even this load for long periods.

If you will want these three things on together regularly then you need someone to look at the supply to the cabin (which is the limiting factor) and see what can be done. There may well be simple solutions but a lot more info is needed to say something is safe.

When you say ring circuit, is it actually a complete loop or a more common daisy-chained (radial) socket circuit?
 
The simplest solution is probably turn the heater off while sawing!

As the others have said, you are likely pushing the circuit design as heating generally consumes a lot of power. I'd expect if you look at the ratings on the extractor and the heater and add up the power in watts, and then add 2000 for the saw you'll be at over 4600 watts which in simple terms is the peak limit of a 20A circuit, and it shouldn't be running with even this load for long periods.

If you will want these three things on together regularly then you need someone to look at the supply to the cabin (which is the limiting factor) and see what can be done. There may well be simple solutions but a lot more info is needed to say something is safe.

When you say ring circuit, is it actually a complete loop or a more common daisy-chained (radial) socket circuit?
It's a sub board in a cabin fed by a 10mm swa 3 core, at about 20meters from the main board feed. The cct is a true ring cct wired with 2.5mm cable. Not a radial.
 
What ever you do,do not change the RCBO to a 32amp.The 20amp is there to protect the cable.You are basically overloading the circuit.As Plugsandsparks says use the saw first or unplug other items while using the saw.
32amp is the normal rating for a 2.5mm ring final ?
 
Is it a B-curve or C-curve? If it is just the peak start-up that is tripping it then changing to 20A C has less concern about the specifics of the cable feeding it.
 
I would not be putting a 32a rcbo just because its been suggested by someone I don't know on an Internet site.
A 32a rcbo may be fine or it may be dangerous. You wouldn't know without further tests. I always think there must be a reason why someone has chosen to put a 20a on what seems to be a ring.
The 20a type C suggestion is good, assuming you can get an EFLI result low enough.
 
I would not be putting a 32a rcbo just because its been suggested by someone I don't know on an Internet site.
A 32a rcbo may be fine or it may be dangerous. You wouldn't know without further tests. I always think there must be a reason why someone has chosen to put a 20a on what seems to be a ring.
The 20a type C suggestion is good, assuming you can get an EFLI result low enough.
The 20amp was first used as it was spare and we did not need any heavy loads so it would have been fine. The correct fuse rating for the ring would have been a 32amp RCBO. So fitting one would be OK as it is a true Final Ring cct. However I like the idea of the C curve as I had forgotten about that characteristic.

( For those who may be reading this B Curve RCBOs trip between 3-5 times full load current and are mainly used in residential applications where loads are resistive e.g. lighting fixtures, domestic appliances with low surge levels.
C Curve RCBOs trip between 5-10 times full load current and are intended for high-level overcurrents. They are the normal choice for commercial and industrial applications where fluorescent lighting, motors etc. are in use.)

However I have come across this, and will be installing as it aids the saw as well. A Soft Start Module.

In addition as we may put further power tools in now I think a C curve RCBO will be in order.

Many Thanks for your reply as this has prompted many solutions and my further understanding. It puts me in a much better position when inviting quotes from electricians.
 
I would not be putting a 32a rcbo just because its been suggested by someone I don't know on an Internet site.
A 32a rcbo may be fine or it may be dangerous. You wouldn't know without further tests. I always think there must be a reason why someone has chosen to put a 20a on what seems to be a ring.
The 20a type C suggestion is good, assuming you can get an EFLI result low enough.
Working on the principle that the information the OP has given us is correct then a 32a would be a good solution.
They said that it is a ring and the 20a was installed at the time as that was what they had to hand.
If the installation paperwork verifies this then I see no issue.
My personal advice would be to get a local sparky to do the swap so they can carry out required tests etc. and ensure the correct part is installed.
Obviously there is no such thing as a 10 minute job :D but this is pretty close. :)
 
Working on the principle that the information the OP has given us is correct then a 32a would be a good solution.
They said that it is a ring and the 20a was installed at the time as that was what they had to hand.
If the installation paperwork verifies this then I see no issue.
My personal advice would be to get a local sparky to do the swap so they can carry out required tests etc. and ensure the correct part is installed.
Obviously there is no such thing as a 10 minute job :D but this is pretty close. :)
OP replied before I posted mine. >.<
 

Reply to Table Saw trips RCBO in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top