Hi,

Thanks for your patience with me - I am a trainee.

So I have got a 2.5 ring in a 20mm PVC conduit. 2 multicore cables enclosed means that according to table 4C1 on page 443 I have to apply Cg of 0.8 to the tabulated current.

So I know that must be > or at least = to In/Cg - (Appendix 4 reg 5.2 equation 5 page 426)
So my It is 32/0.8 - 40A. In the case of a ring then this is 20A per leg effectively for cable selection.

So far so good - I think anyway.

So off I go to table 4D5 on page 456. Selecting a 2.5mm for Ref method B - 23A. I get it.

But in table 4D5 the cable (in this case 2.5mm) has been already derated from 27A clipped direct to 23A for my reference method.

So am I?

A - applying the derating twice?
B - or is it that table 4D5 is just confirming that in a conduit the 2.5mm cable can carry the current I want (at 70deg)?

I think its B - but I have got in a twist with it.

Cheers,
 
Hi,

Thanks for your patience with me - I am a trainee.

So I have got a 2.5 ring in a 20mm PVC conduit. 2 multicore cables enclosed means that according to table 4C1 on page 443 I have to apply Cg of 0.8 to the tabulated current.

So I know that must be > or at least = to In/Cg - (Appendix 4 reg 5.2 equation 5 page 426)
So my It is 32/0.8 - 40A. In the case of a ring then this is 20A per leg effectively for cable selection.

So far so good - I think anyway.

So off I go to table 4D5 on page 456. Selecting a 2.5mm for Ref method B - 23A. I get it.

But in table 4D5 the cable (in this case 2.5mm) has been already derated from 27A clipped direct to 23A for my reference method.

So am I?

A - applying the derating twice?
B - or is it that table 4D5 is just confirming that in a conduit the 2.5mm cable can carry the current I want (at 70deg)?

I think its B - but I have got in a twist with it.

Cheers,
It is neither in the sense it isn't the same rating factor applied twice.

Table 4C1 is grouping and 4D5 is current carrying capacity for different Installation methods, they are 2 separate things. You will see in the side note to Grouping that Item 1 can be used with Refence Methods A to F.
 

Reply to the thread, titled "Tabulated Current - Trainee - Am I applying derating factors twice?" which is posted in UK Electrical Forum on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Thread starter

Joined
Location
South UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Tabulated Current - Trainee - Am I applying derating factors twice?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1

Thread Tags

Thread statistics

Created
ceeeee,
Last reply from
PS Electrics,
Replies
1
Views
69
Back
Top