Learning every day.I wouldnt say it’s the best way if there is spare way on a RCD protected way that shares the same side as a socket circuit for example. It would actually be non compliant due to how long the inverter takes to shut down which can be up to 5 seconds under G83.
If I've understood correctly - in a dual RCD board if they've attached PV invertor to MCB under one of the RCDs, if that RCD detects a fault and trips, great. But the invertor continues to put 230V onto the common MCB busbar. So ADS has not been achieved (!!!).