Tail sizes - max demand suggests too small

L

LlandrilloSpark

Fellas

Im just writing up the 5 flats I inspected last week, all the service heads/fuses are new to within 3 years, the cut out fuses are all 100A and tails all 16mm, I know discretion is sometimes needed in this area, on some flats the Max demand reaches 90-100A whilst in others 65-75A, would anybody agree that this is basic circuit design and those with the high max demand need the tails changing?

cheers
 