s1m0n

Hi,

I have recently replaced a consumer unit on a TT earthing arrangement.
I went down the local Building control route, no problem so far.

Sent in the completed certificate, but got it declined with this stated on the paperwork.

"TAIL SIZES NOT GIVEN THEREFORE UNABLE TO DETERMINE IF EARTH CABLE IS CORRECT"

I use the certifcates from BS7671 (short version)

I can not see any where that asks for the Tail sizes.

any input welcome.

Confused :confused:
 
Was it the Electrical Installation certificate you used. If so then it does ask for the size of the supply tails, if it didnt you have filled in the wrong form for the job. I assume the short version you refer to is the one that only requires one signature for construction, design and testing etc, even so this also does have the field to complete for the supply tails size.

regards...........Howard
 
Hi Sirkit breaker,

it is the one with just one signature for design,constructionand Inspecting & testing,

do you know exactly where on the form,

Thanks in advance

Simon
 
Was it the Electrical Installation certificate you used. If so then it does ask for the size of the supply tails, if it didnt you have filled in the wrong form for the job. I assume the short version you refer to is the one that only requires one signature for construction, design and testing etc, even so this also does have the field to complete for the supply tails size.

regards...........Howard

There is no field for supply tail sizes, only Earthing Conductor and Main Protective Bonding Conductor sizes.

[ElectriciansForums.net] Tail Sizes on EIC
 
Hi Graeme,

I can only see 2 pages of the Long form EIC, checked in BS7671 regs and GN3

Am I not looking in the right place?

Simon
 
Page 3 of the full EIC has a box for supply details where tail sizes and materials are listed.....

Are you talking about the same EIC? We're on about the model certificates from the BRB.

Just been right through the PDF and the EIC doesn't have a page 3. Page 3 would be the schedule of Inspections.
 

Attachments

  • [ElectriciansForums.net] Tail Sizes on EIC
    Page 1.JPG
    139.1 KB · Views: 18
  • [ElectriciansForums.net] Tail Sizes on EIC
    Page 2.JPG
    129 KB · Views: 12
  • [ElectriciansForums.net] Tail Sizes on EIC
    Page 3.JPG
    158.4 KB · Views: 8
  • [ElectriciansForums.net] Tail Sizes on EIC
    Page 4.JPG
    101.7 KB · Views: 11
Last edited by a moderator:
A copy of page 1 of one of my EIC, page 2 is all the usual boring crud also!
.
.
.
.
[ElectriciansForums.net] Tail Sizes on EIC


Just to add, Simon if you would like me to post you a couple of the complete set of forms I will, these are non 'club' forms as I prefer these!

If you want a couple please PM me your address! Stick a couple of quid in the local charity box to cover postage!
 

Attachments

  • [ElectriciansForums.net] Tail Sizes on EIC
    img009.jpg
    459.8 KB · Views: 28
Last edited:
There is no field for supply tail sizes, only Earthing Conductor and Main Protective Bonding Conductor sizes.

[ElectriciansForums.net] Tail Sizes on EIC

I have never seen that form. The ones i fill in are the full EIC single signature, and these do have the relevant fields to fill in for the size of supply tails, protective conductors and all the rest of it.

Cheers.........Howard;)
 
I have never seen that form. The ones i fill in are the full EIC single signature, and these do have the relevant fields to fill in for the size of supply tails, protective conductors and all the rest of it.

Cheers.........Howard;)

You should have seen that form.

It's the one from the back of BS 7671 ;)
 

Reply to Tail Sizes on EIC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top