Hello all.

About to do a CU change and from the pre works visit it looks like the 16mm T&E from the meter is run 3m to the CU behind the skirting board. No mechanical protection seen. TNS. Ze = 0.28ohms.

This clearly isn't acceptable and I shall advise getting it changed but my question is would you still change the CU? I've never quite seen the logic in not changing it. In this case it would go from a BS3036 board with no RCD to Amd 3 board with RCD protection.

Ps.. 2 more questions.

2. Can 16mm T&E have a 10mm earth (it looks like 10mm and I thought 16mm had a 6mm cpc)?

3 . The gas is bonded in the correct position with 10mm but this goes to a bonding clamp around the supply cable, just above the TNS connection. I've never seen this before and it looks bodgy. Is this acceptable?

Cheers.
 
Last edited:
Thanks for all the replies guys. I have given her a quote for the CU change and the extra work. She has said she will get it all done but can only afford the CU change now (and other work next month). I believe her so intend to carry out the CU change.

I do take on board what the electricians above have said regarding not carry out the work until other work has been done, and I would have refused the CU change if she had point blank refused to have the additional work done, but she seems genuine and I believe I will be back next month. Maybe naive, maybe not!

Did anyone have any thoughts on the bonding clamp on the TNS going to the gas (see point 3 in my OP)?
 
Hi - can't you establish a new MET and connect it from there?
I can and will, just wondered if any one had seen this before and really whether it's acceptable. It certainly gives a very low continuity reading to the gas pipes!
 

Reply to Tails (or rather T&E) behind skirting. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top