Hi, just a quick question I am upgrading a cu and partial rewire. Now the tails from the cutout are 16mm and go in to a teleswitch, they then comeout and go in to a multiwatt reader then in to the ccu. Obviously I want to use 25mm tails after the meter so do I get the electric board out to upgrade there part? Can the teleswitch be removed by them ? At my house supply comes in to cut out into meter then in to isolator then in to cu.! Any advice appreciated I am new to the game also so be kind
 
You would be wasting money getting them out to change their part, they won't be interested, 16mm is fine for almost all domestic applications, you may well find you have a 60A or 80A fuse anyhow. What they have between their cut-out aand meter is their property, I wouldn't even worry about it.
 
It's not your job to worry about the size of the tails on the supplier's side. And are you sure the tails on the consumer's side need 'upgrading'? Is the teleswitch no longer serving a purpose? If not, you would be lucky to get them to remove it. Depend who the DNO is, around my parts they would only remove when the meter is due to be replaced, unless it is in some way dangerous!
 
There is a mention of min. 25mm tails in the OSG, but no reference to any reg or reason as to this (if memory serves me), it is another page that may well be more useful as toilet paper. It's almost like they're dumbing things down so much in that OSG, like, "If we say to use too big every time then nobody can use too small. Doesn't matter if the reader knows how to work out the appropriate size for themselves or not.". Hic.
 

Reply to Tails upgrade in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
787
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
701
  • Question
I think it's more towards what the future brings with them and their ability to measure true power. Half remember a video from bigclivedotcom that...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top