Take it or leave it | Page 2 | on ElectriciansForums
Discuss Take it or leave it in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
It's not really a problem I have to deal with very often.
Usually when I tell my customers what is required, they accept it and that's that.
Occasionally I get a difficult one, and then I just do it as they request, as long as it's safe.
Then if there's any problems. I just say 'I told you so'.
In your situation, I would explain that the cable and the MCB require uprating, as the shower has a higher rating
I would then explain that if I don't replace the cable, I cannot uprate the MCB, and there is a possibility that the MCB will trip if the shower is used for too long.
Note the departure on the MWC, job done.
In a couple of months time, there will be a very good possibillity that they will be on the blower begging for you to come and replace the cable and the MCB.
More work, more money.
I was taught that cable buried directly into standard masonary and plaster is method C. However I've just looked at table 4A2 and it makes mention of cables buried in a thermally insulating wall, but not the more common occurance of cables buried in plaster. As this method is extremely common isn't it odd that 7671 doesn't cover it?
Assuming I was taught correctly and the 6mm cable is clipped direct or buried in plaster or behind normal tiles, then its ccc is 47A and so a 9.5kW shower is fine on this cable with a 40A mcb.
If the cable passes through a loft and you have methods 100 or 101, then that is different. In this instance I would look to re-route this section of cable above the insulation layer and use a 4 inch pipe to maintain an air gap around the cable where it must pass through the insulation.
bearing in mind the safety factors biult in to the rated ccc in BS7671, i would have no hesitation in rating 6mm in a nmasonry wall at 40 - 45A. and protect with a 40A type B MCB.
Electrician's Guide to the Building Regs says;
Method C; clipped direct or embedded in plaster.
Method B; run in conduit or trunking installed on, or in, plaster, masonry or the like.
Laurie
Reply to Take it or leave it in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Very technical :D