Thought I share this with you,arrived on site to start a 1st fix on school classrooms,saw temp electrics to cabins,for site agent & mess rm.First impression rough,sy cable used ,we all know hassle with that,looked at DB ,hanging from the DB a 10 mm earth cable,not connected.Asked site agent who did the temps,it wasn't our company,so carried on with my other works.
later on,site agent wants some temp external power installed,& wants us to do it.
So installed power,& tested,Supply cable loop impedance,at DB did not comply,& would not disconnect on fault conditions.
Earth for temps,Swa sheath used,does not comply.
Earth cable from DB not connected to earth rod.
So,told site agent,he called guys who installed electrics,they phone me,the complete nonsense & crap from the electrician & his boss,I really could not believe,giving me its ok, the mcb will be fine you are allowed 2 ohms on a 40 amp c type.
Anyway the 2 electricians come over,spoke to them about my opinions,that went down well,No,they put a rcd upfront,sat in the van,still no electrode fitted,frustrating, does anyone care.
By the way it's a pme system.
 
Will they even bother looking,the company who employed them think they are wonderful,haven't yet seen certificate,still no proper earthing system,still Pme to metal cabins & no real main bonding.
 

Reply to Temp supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
400
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
959
  • Question
https://www.edwardes.co.uk/products/mk-k1257whi-logic-plus-1gang-13amp-non-standard-dp-switch-socket?gad_source=1&gclid=EAIaIQobChMI7POp_pHFhgMVk5J...
Replies
1
Views
355

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top