Temporary building supply | on ElectriciansForums
Discuss Temporary building supply in the UK Electrical Forum area at ElectriciansForums.net
Kent
Evening all,
Does anyone now what the correct arrangement for a temp building supply is these days. I am just about to start first fix a new build and am going to have to provide temp supply . In the past I have put in an Earth rod, tails onto a switch fuse/dp isolator and out into a little board with rcd as main switch. Dno can then connect to the switch fuse /dp isolator etc. One of my colleagues suggested that they now would
Like an s type rcd before the consumer unit as it is a TT. Does anyone know what they like these days as I have tried to get in contact with power networks but I am still waiting for a reply
Many thanks
up front RCD 100ma S type, then into consumer unit 30ma RCD protection at that point, earth rod & tested with results would be good.
might get away with 30ma rcd unit at board without the 100ma but they might not connect.
3 phase definitely wont connect you without the 100ma trip
Reply to Temporary building supply in the UK Electrical Forum area at ElectriciansForums.net
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...