GBDamo
After the YY burnout posted in;-
I intend to rewire and have given a rough quote.
Background.
These lights are head height wall mounted intended to illuminate the engine bay of a car, 10 workstations in a large workshop.
At present they are through wired through each other so, if the cable goes in one they all go upstream.
The reasoning behind my intention is that should one fitting go then the a fuse will blow highlighting the damaged fitting and allow continuity of works with the other lights.
Also allows for the damaged light to be worked on without isolating the circuit (FCU option).
Intention
Is to re-wire in galv conduit in 2.5 singles running the whole circuit off a c25 MCB.
And
1, give each fitting it's own FCU fused to 3A
or (see Questions)
2, Fit a 5x20mm fuse holder to an IP65 JB and use a quick blow fuse.
Then flex down to each fitting from the FCU/JB.
The customer is keen on this approach if it is reasonably feasable.
Questions
1, I can't find a source I trust for a 3A BS1362 curve, BBB don't have it so can't be sure the BS1362 will go before the MCB, any pointers?
If the above is a non starter;-
2, Does anyone see an issue with the approach of fitting fuse holder to a JB and 5A F rated fuse, this route also allows me to down rate the circuit CSA and MCB and ?
Dodgy trade pictures for your amusement! - 1 Million Views! | Page 160 | on ElectriciansForums
Find Dodgy trade pictures for your amusement! - 1 Million Views! Advice and Help. How-to Dodgy trade pictures for your amusement! - 1 Million Views! in the UK Electrical Forum advice boards on ElectriciansForums.net Est.2006 | Free Electrical Advice Forum. Dodgy trade pictures for your...
www.electriciansforums.net
I intend to rewire and have given a rough quote.
Background.
These lights are head height wall mounted intended to illuminate the engine bay of a car, 10 workstations in a large workshop.
At present they are through wired through each other so, if the cable goes in one they all go upstream.
The reasoning behind my intention is that should one fitting go then the a fuse will blow highlighting the damaged fitting and allow continuity of works with the other lights.
Also allows for the damaged light to be worked on without isolating the circuit (FCU option).
Intention
Is to re-wire in galv conduit in 2.5 singles running the whole circuit off a c25 MCB.
And
1, give each fitting it's own FCU fused to 3A
or (see Questions)
2, Fit a 5x20mm fuse holder to an IP65 JB and use a quick blow fuse.
Then flex down to each fitting from the FCU/JB.
The customer is keen on this approach if it is reasonably feasable.
Questions
1, I can't find a source I trust for a 3A BS1362 curve, BBB don't have it so can't be sure the BS1362 will go before the MCB, any pointers?
If the above is a non starter;-
2, Does anyone see an issue with the approach of fitting fuse holder to a JB and 5A F rated fuse, this route also allows me to down rate the circuit CSA and MCB and ?