GBDamo

Been doing some maintenance/service work on AC compressors and one thing that concerns me is the amount of heat at all the various terminals along the start and run circuit.

In brief the the current draw should be anything from ten to twenty amps but I'm often seeing readings 50% higher that this. When viewing the circuit using an FLIR thermal imaging camera there is a lot of excess heat at the spade crimp terminals.

Removing the spades, closing them with pliers and replacing them greatly reduces the heat and resistance but I've noticed all are slightly tarnished.

I'd like to find a none abrasive cleaning solution and a grease that will improve conductivity as well as prevent further corrosion.

I have googled a few products but can't see the sense in reinventing the wheel, i.e. this must be fairly routine in industry and there must be many maintenance sparks out there who do these routinely.

If so can your share some advice or tips for improving the above situation

Thanks

Damion.
 
Some of these terminals are coated to improve electrical conductivity,
if this coating is worn then conductivity will be reduced
Have you tried just replacing these terminals with good quality one's.
I'll certainly look to replace any female that becomes slack or loose. Unfortunately the males are fixed on various PCB or other components so cannot be replaced.
 
We do quite a lot of HVAC work and from experience the compressor push-on terminals that give overheating problems are usually because the original installer has been ham fisted and causing them to be loose when they were first fitted.

As mentioned above, once this occurs the damage is permanent because they overheat and lose their ability to hold tension even if you compress them again with pliers. If a terminal has become tarnished on both the male and female side due to overheating I'd actually cut the crimp-on terminal off the wire side, clean up the side of the terminal that's fixed and solder it.
 
i agree marvo
as long as there is not an excessive amount of vibration once the crimpon terminal is connected you can also paint the connection with a varnish (like nail polish) to prevent air and moisture exposure.
it does withstand heat fairly well.
down side of it is it's a real bear to remove from the terminals
you can also paint over the connection with silicone grease
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Terminal corrosion on AC compressors.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19
Unsolved
--

Advert

Thread statistics

Created
GBDamo,
Last reply from
gnuuser,
Replies
19
Views
5,349

Advert

Back
Top