Looks like I referred to table F5 (pvc multicore cables)

So in table F6 (flat insulated and sheathed pvc) I have a combination of reference method 100* and also partly ran in trunking.

10mm Reference method 100* allows a total of 45 amp. The shower 41amp.

I'm still happy with the choice.
 
Looks like I referred to table F5 (pvc multicore cables)

So in table F6 (flat insulated and sheathed pvc) I have a combination of reference method 100* and also partly ran in trunking.

10mm Reference method 100* allows a total of 45 amp. The shower 41amp.

I'm still happy with the choice.
What protective device dude?
 
40amp.

However the actual current drawn will depend upon the voltage of the supply. 230 = 41amp 240 = 39 amp. The actual voltage I measured was 243 (39 amp)
 
40amp.

However the actual current drawn will depend upon the voltage of the supply. 230 = 41amp 240 = 39 amp. The actual voltage I measured was 243 (39 amp)
ohm's law says the opposite. just you get more kW @ 240V than @ 230V.
 
You're right mate, but power is provided for a given voltage, in the UK it will be 9500W at 230v. Therefore if you do put 240v up it, it will actually produce ~9800W of power.

Ah. Makes sense. Thanks Hightower

So upon checking with my dad on the shower he's confirmed it's actually a 8.5kw.

So 6mm could have been fine, however I'm still glad I changed it because from the switch to the shower the cable was actually some kind of white flat twin and earth with no markings on it. God knows where that's comes from.

So to summarise:

37A shower, at nominal voltage ;-)
10mm T&E (part in trunking and part in the loft under insulation below 100mm)
45A double pole switch.
40A breaker
 
Probably IMO the best choice to install the 10mm even though the shower is only rated at 8.5KW it will allow for any future upgrades to a more powerful shower with the correct testing beforehand obviously. All new builds install 10mm as standard nowadays so for me it was the right thing to do as I have been taught an electric shower is probably the highest load on any domestic install.
 

Reply to Terminating 10mm in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top