Evening all. I have to supply a garage conversion with a 16mm armoured running 40 meters away from the main house. I was thinking about coming off the Henley blocks (in the meter cupboard) into a TIME DELAYED RCD board, with a 63 amp Mcb, then glanding the 16mm armoured into the board. I was thinking About putting a separate meter box next to the existing as I know sweb get funny about it all Is this the Best way to go about it ?
If the existing supply has a TT earthing arrangement then you'd certainly need an S type 100ma RCD for additional protection to the SWA submain due to the likely high impedance and relatively low earth fault current. But with a TNCS or TNS supply the additional RCD would be unnecessary.
If all you need is a means to make off an armoured without the faff of a box, present the gland into a female conduit bush, sleeve the conductors with decent heatshrink, fill the bush with resin and use the banjo to fix it to the wall. Tony taught me that one.
I have seen it done like this in the past however it needs to be terminated into an enclosure.
[ElectriciansForums.net] Terminating armoured in meter box
Agreed, no OCD for the armoured cable, not glanded into enclosure, conductor ID, exposed singularly insulated conductors, SPD's??? etc etc........
It goes without saying....... but I'm on about everything being open and unsealed.
It indicates that the isolator has actually been installed, with the outgoing swa having originally been directly from the meter???
Reply to Terminating armoured in meter box in the UK Electrical Forum area at ElectriciansForums.net
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX