Need to use a pair of 6mm T&E in parallel to run an 10.8kW electric shower. Both same length and same route, will be joined to a single 10mm at the load end, and protected accordingly.

Can anyone recommend a terminal box which I can use for this?

I don't fancy putting a pair of 6mm into one side of a 50A chocbloc, but something like a Henley seems a bit OTT...
 
They both go into the wall at the same place and come out in the loft at the same place. They were installed at the same time and are pretty much the same when metered, so I'm confident they're on the same route.
Did you test the L+N resistance of both cables? What were the results/how big is the difference?
 
Last edited:
The push fits I've used, they arent as good as wago in my opinion.

The fire nuts I wouldn't touch and I don't think any self respecting electrician would.

The example push-fit are only to 2.5mm stranded anyway, Wago do to 6mm in leaver for sure, but I think the OP needs to attach to 10mm eventually.

Agree on the fire nuts!

The big 100A Henley style blocks seem overkill, I would generally use DIN rail stuff as you can get jumper bars to common them (so using two DIN terminals gives 4 connection points), and the earth style DIN terminals also ground to the rail itself.

Look on CEF for IVBWKN10-10 (10 way jumper bar, can be cut down as needed) and WKN10U (grey terminal) and WKN10U BLUE (same, but blue if you feel the need to colour code them for neutral). One jumper bar and 6 terminals would do each end.

If using the WKN10SLU earth terminals to common earth via the rail, then one 10-way jumper bar would do both ends (need 4 links of 2 terminals, so 8 from the bar).
 
Last edited:
I think its Ashley that do a large brown 60 Amp jb, I'm sure that would accept all the conductors you require to join.
Yes, much easier than DIR rail!

A quick search on CEF shows "Scolmore Click 60A" box apparently takes up to 25mm cable so should do the job in a much simpler and cheaper way. No idea it if could be considered "maintenance free" to be hidden though, I doubt it given the screw terminal fixing method.
 
For general paralleling and commoning duties where screw terminals are suitable, I often use European-style commoning blocks such as the Cembre range. Here's another Italian example - I've used these and they are well made and substantial. The particular type in this link has four entries for up to 6mm² and two for 6-16mm² and can be mounted to a DIN rail with a clip.
6-16mm² commoning block from RS

Here is another style from Legrand that clips directly onto the rail. These are good too although lack the support of the entry spout to prevent cable movement in the terminal.
4-way Legrand 16mm² commoning block

Personally, I would not try terminating two conductors in a shower isolator for the purpose of paralleling. The regs and common sense require the paralleling connection to be made in such a way that it is unlikely for the continuity to be lost. We are all familiar with terminal burnouts, due to high resistance contacts and cables coming loose with manoeuvring the switch into place, so I venture that putting the two into the isolator terminals doesn't really meet that criterion.
 
Last edited:
For general paralleling and commoning duties where screw terminals are suitable, I often use European-style commoning blocks such as the Cembre range. Here's another Italian example - I've used these and they are well made and substantial. The particular type in this link has four entries for up to 6mm² and two for 6-16mm² and can be mounted to a DIN rail with a clip.
6-16mm² commoning block from RS

Here is another style from Legrand that clips directly onto the rail. These are good too although lack the support of the entry spout to prevent cable movement in the terminal.
4-way Legrand 16mm² commoning block

Personally, I would not try terminating two conductors in a shower isolator for the purpose of paralleling. The regs and common sense require the paralleling connection to be made in such a way that it is unlikely for the continuity to be lost. We are all familiar with terminal burnouts, due to high resistance contacts and cables coming loose with manoeuvring the switch into place, so I venture that putting the two into the isolator terminals doesn't really meet that criterion.

Interesting to see that RS part, never know about it so thanks!

As well as the one you linked to with 4 * 2.5-6mm and 2 * 6-16mm holes, RS also stock a 4-way common block with 4 * 6-16mm that is cheaper (but in packs) as:


I also don't like the idea of using the isolator's terminals. At least some of the junction boxes allow the cables to be clamped as they enter for support, and conductors terminated with double-screws for greater reliability.
 

Reply to Terminating parallel supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
290
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
276
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top