I have only every done indusrial, from pat testing to panel building, plc programming or installation never house bashed. just been asked to a inspection on one of the 5 factories I look after and I wanted to make sure I am not being too harsh on some of the faults i am finding. most of them are codes 1, or 2's for example 30Amp fuse wire in a 15 amp carrier or 2 X 100A fuse wires in a 100Amp carrier or borrowed neutrals, box lids / trunking lids missing, just wanted to clear up one or 2 things.From the questions you are asking, it doesn't sound like you have any industrial experience-do you know anyone with industrial experience that can help you?
It's often the case on larger installations where the 'leg' from the DB will be a higher CSA before gradually reducing to allow for volt drop etc. as long as the protective device is rated to suit the lowest CSA then there is no code (why would there be?)
GN3:-
1.2 Required competence
The inspector carrying out the inspection and testing of any electrical
installation must, as appropriate to his or her function, have a sound
knowledge and experience relevant to the nature of the installation being
inspected and tested, and BS 7671 and other relevant technical standards.
The inspector must also be fully versed in the inspection and testing
procedures and employ suitable testing equipment during the inspection
and testing process.
Not 'having a go' but you are being paid for your expertise and experience.