Test Cert. | on ElectriciansForums

Discuss Test Cert. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Mark.W

-
Joined
Apr 18, 2009
Messages
1,005
Reaction score
37
Location
Swindon, Wilts
Morning chaps!

I was just wondering... If you install a new socket on an existing ring or anything on an existing circuit in fact, how would you go about putting your test results on the installation certificate? Surely you would then be testing someone elses work?

Thanks for the advice!

Mark
 
I quote BS7671: "The minor works electrical certificate is intended to be used for additions & alterations to an installlation that do not extend to the provision of a new circuit. Examples include the addition of a socket outlet or lighting point" etc etc..
Here's the Caviat: "Appropriate inspection & testing, however, should always be carried out irrespective of the extent of work undertaken."

So yes, you may be testing someone elses original installation but as you touched it last you are responsible. Best thing to do is to test it before you carry any work on a circuit, that way you will also be able to know that any subsequent faults (God forbid) be present.
 
Best Practice is to carry out a full set of tests on the existing circuit before work commences. This proves the existing circuit is safe and complies with BS7671.

If there is a fault you can either quote extar cost for fault finding or Make safe if necessary and inform client of the fault in writing.

If everything is OK complete the work and then carry out inspection, Test and correct certification depending if the work is notifiable or non-notifiable under Part P.
 

Reply to Test Cert. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
749
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

We wouldn't be at all surprised I have been a QS for 25 odd years.
Replies
7
Views
813
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top