Guest 004

Can anybody advise how much test current is applied when using a 1552 meggar on Zs.

Somebody suggests that it could be as high as 6 amp's?

Thanks
 
25A on hi. 15mA on no trip. the 25A current sometimes causes breakers to trip.
 
This is a live test so i think the instrument allows a 40ms window of 25A or 15mA to flow into the machine rather than generating it itself.
However, some testers will do a N-PE loop test where the instrument generates the necessary current.
 
If you look in GN3 it gives the spec for this test kit, irrelevant of make and model, it must induce a minimum current for a minimum length of time. I will let you look it up. I am not trying to be clever, but GN3 will answer all of the basic test and inspection questions asked, and if you are delving into the insp and test world, treat yourself, its only about ÂŁ25.

Cheers...........Howard
 

Reply to Test currents applied by a loop tester in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I don't think it will work with only one stake unless some meters have different operating parameters. It doesn't necessarily have to be a stake...
Replies
3
Views
1K
I'd speak to an independant company about fixing this, you'd expect it to be a relatively simple adjustment and not require much in the way of...
Replies
12
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top