that'd be a RFC then.
Exactly! I read it as an RFC split across 2 MCB's. Obviously you guys understand what the op is on about..
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss testing 2 radials in one mcb in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
that'd be a RFC then.
When testing a Consumer Unit with two radials feeding one socket on each circuit, wich results would you record on the condition report?
that'd be a RFC then.
it's 1 MCB with 2 legs going out. each leg to a socket. so basically 2 radial branches. whet would be of concern is if the MCB was a 32A feeding 2 2.5mm legs, not configured as a RFC.
debateable.
u could only class it as a radial with parallel conductors ifboth cables are of the same length and follow the same route.
Check both and record the higher of the two readings
This is what I thought. . .
why the two sockets are wired sepratly i dont know..
cheers for the replys!
This is what I thought. . .
why the two sockets are wired sepratly i dont know..
cheers for the replys!
Couple of reasons maybe they were 2 separate circuits remember 30 years ago electric showers were not the norm all of a sudden they become affordable and they need a spare way in the basic 6 or 8 way 3036 CU. Another reason is an additional socket or outside security light where it is easier to wire from the CU . Wait until you get a socket spurred off a ring circuit in the CU
Tel's point -2 separate sockets on two cables from one OPD - only one circuit.Ah, so 2 separate sockets on 2 circuits