C Chris1234 - Jun 24, 2019 #1 Hi, am I right in thinking that a Megger 1552 can’t test RCD’s at more than 1000mA? Therefore a 5x test on s 300mA RCD can’t happen?
Hi, am I right in thinking that a Megger 1552 can’t test RCD’s at more than 1000mA? Therefore a 5x test on s 300mA RCD can’t happen?
Strima - Esteemed Arms Jun 24, 2019 #2 5x only required for RCDs providing additional protection. So you only need to test at 1/2x and 1x. Upvote 0 Downvote
telectrix - Mentor Arms Jun 24, 2019 #3 there is no requirement to test a 300mA RCD at x5. Upvote 0 Downvote
D Deleted member 26818 Jun 24, 2019 #5 There’s also the safety aspect of not sending 1.5A down to earth. Upvote 0 Downvote