Hi there,

i was called to a job by a customer to replace a distribution board that had suffered water damage within a farm building.

The DB i was presented with was 2 - phase, with a measured 250v per phase and 480v between phases. I have never seen these before and no-one in the wholesalers has either, so locating one is a problem in itself.

More importantly though, my test equipment will not carry out a PFC test on 480v equipment. Can i do this through calculation and is it done in the same manner as per 3 phase i.e

(pfc=v/ze)*2

??

Thanks in advance and any information regarding 2-phase 480v installations is much appreciated.
 
Dont't know alot about it but 2 phase just means you have 2 seperate 240 volt single phase supplies, a common neutral and earth!

You can obtain PFC by enquiry!

Hope this helps!:D
 
Is it not possible to use a standard 3 phase board and connect the 2 x phases and neutral to the same and mark up the 3rd phase ways as blank? / unused
Just a thoought...

is this possible ?
 
Hi there,

i was called to a job by a customer to replace a distribution board that had suffered water damage within a farm building.

The DB i was presented with was 2 - phase, with a measured 250v per phase and 480v between phases. I have never seen these before and no-one in the wholesalers has either, so locating one is a problem in itself.

More importantly though, my test equipment will not carry out a PFC test on 480v equipment. Can i do this through calculation and is it done in the same manner as per 3 phase i.e

(pfc=v/ze)*2

??

Thanks in advance and any information regarding 2-phase 480v installations is much appreciated.
Must be very close to supply transformer,normally you would expect 240/460volts.But I don't see any
reason why you couldn't treat it as 3 phase provided you have it suitably labled up.You should try and balance your load as much as possable.It's unlikely that you would have many loads using both phases,
though I have seen a 400volt single phase welder,and it is also possable to get water heaters running at the higher voltage...They have similar set ups in other countries,eg Canada and USA etc,I think they are known as Edison or split phase as other poster suggests. I think we are lucky over here in that 99% of our supply over here has been standardized to 230/400 volt.
 
Yep, standard 2 phase 3 wire install and common on farms agri etc. As others have said, treat as 3 phase unless both phases are being used, ie 2DB's, then as 2 seperates.

Steve.
 
The shop i have just finished was a 2 phase 3 - wire install, and that was in the middle of town.

Reason being,according to the DNO, there were only 2 phases available in the street, apparently.
 
The shop i have just finished was a 2 phase 3 - wire install, and that was in the middle of town.

Reason being,according to the DNO, there were only 2 phases available in the street, apparently.
Hi,
There seems to be a little confusion over split phase and two phase.I will attempt to provide clarification.230/460volt would be split phase where the 460 volts are tapped off a supply transformer from a single phase sourse,ie the primary would be supplied at a higher line voltage(1 live wire and an
(earthed)neutral.On the secondary side the windings are centre tapped to earth giving 230volts from each leg to earth....and 460 between lines.
So on a two phase system(derived from two of your three phases) 230/400volt your voltage between phases is approx 400 volts..and your
voltage to earth is 400 devided by square root of three giving approx 231volts.
I came across one years ago in the centre of town but I'm not sure now which of the above categories it fell in,but 400,OR 460 volts on their own are pretty limited in their usage ie,no good for three phase motors.
 

Reply to Testing 480v system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
415
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
961

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top