Thanks all for the replies.... Im going to measure the earth fault loop impedance at the isolator for each phase and add R1+R2 to this reading and document all readings on the test cert. From reading the posts this seams to be the way to go....
 
Most 3 phase motors don't have neutrals.

With respect to performing Earth Fault Loop Impedance at the isolator of a 3-phase motor (with no neutral) fed through a VSD I have two queries.


1. Can the test be perfomed with the VSD in the circuit or should it be by passed or perhaps measure EFLI at the incommer of the VSD and calculate R1 + R2 for the remainder of the circuit ?

2. My test kit is a Kewtech KT65 which I believe requires a neutral to perform the test or do I get around this ?

I'm open to ideas. Thanks.
 
Kodr... why are you wanting to test the set-up are you doing a EICR if so the testing is the circuit itself not the equipment/controls attached to it... you shouldn't be performing any tests through the VSD, if you are checking the motor i.e. Insulation resistance then ensure the VSD isn't connected. You need to be very careful you dont damage anything if its a control system including the VSD so isolate the load from the circuit and test the circuit only....BS7671 does not cover the machine/motor control system as such although if it was a simple DOL pump on an isolation switch then usually no harm in testing through.
 
BS7671 does not cover the machine/motor control system

True. I'm not including the motor. Isolator in the off position I just want to know if I can perform a EFLI test whist the VSD is connected or should calculate Zs=Ze + (R1+R2), I appreciate VSD are control equipment but what is normal practice to determine EFLI for these circuits.

Also, in cases where I have DOL motor cicuits with no neutral how is test performed without the neutral, my multifunction test kit (Kewtech KT65) requires a neutral.

Thanks.
 
You don't need test results for a motor fed by a VSD. Usually the manufacturers manual will tell you the cable size and max length. Cables feeding motors on VSDs can seem oversized, but it's due to the effects of the changing frequency!
a long lead test would be a good idea, as this would confirm an earth path. It's more important to check the screens, especially on larger motors. I've tested 15A flowing to earth via a screen, and it was brand new, and the engineers were happy.
 

Reply to testing a 3 phase motor for fault loop impedence in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
561
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
936

Similar threads

Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
484
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
519

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top