C

chloebear

Hi All,
I have to carry out some work on an installation that has its earthing run as part of the metal conduit system. This raises a few questions apart from checking to ensure that the conduit, and therefore, the earthing is intact.
(1) using NICEIC paperwork, what do I record for the CPC size?
(2) Checking R1+R2 - what would be the best way to do this? as basically I have no R2 apart from the earthed conduit.
(3) whats the best way of carrying out Insulation Resistance Tests
(4) are there any further recomended tests to carry out for this type of installation
 
(1) Just write conduit or con
(2) Record R2, use a long lead for this
(3) Carry out insulation resistance as normal, just put your croc clip onto the conduit
(4) None really, just make sure all visible joints and connections are good.
 
Hi All,
I have to carry out some work on an installation that has its earthing run as part of the metal conduit system. This raises a few questions apart from checking to ensure that the conduit, and therefore, the earthing is intact.
(1) using NICEIC paperwork, what do I record for the CPC size?
(2) Checking R1+R2 - what would be the best way to do this? as basically I have no R2 apart from the earthed conduit.
(3) whats the best way of carrying out Insulation Resistance Tests
(4) are there any further recomended tests to carry out for this type of installation

Make sure that each accessory has a green/yellow fly lead linking it to the back box, this is a requirement where the containment system is the cpc.
 
As all the others have said but if you want to be a NICEIC blue eyed boy use these figures for your cpc sizes.
Heavy gauge steel conduit to BS 4568 Part 1
16mm diameter= 64.4mm csa
20mm diameter= 82.6mm csa
25mm diameter= 105.4mm csa
32mm diameter= 137.3mm csa

Steel surface trunking to BS 4678 Part 1
50x50mm = 135mm csa
75x75mm = 243mm csa
100x20mm = 216mm csa
100x100mm = 324mm csa
150x100mm = 378mm csa

Pyro 500V light duty
2L1 = 5.4mm csa
2L1.5 = 6.3mm csa
2L2.5 = 8.2mm csa
2L4 = 10.7mm csa
3L1 = 6.7mm csa
3L1.5 = 7.8mm csa
3L2.5 = 9.5mm csa
4L1 = 7.7mm csa
4L1.5 = 9.1mm csa
4L2.5 = 11.3mm csa
7L1 = 10.2mm csa
7L1.5 = 11.8mm csa
7L2.5 = 15.4mm csa
 
They are figures that I'd use for design parameters but I wouldn't expect to see them entered on a test sheet, the NICEIC testing manual records the use of conduit as a cpc as 'con' on the cpc section of circuit details.
 
They are figures that I'd use for design parameters but I wouldn't expect to see them entered on a test sheet, the NICEIC testing manual records the use of conduit as a cpc as 'con' on the cpc section of circuit details.

Very true and I agree. If you are using software such as Amtech then you would not be able to enter con, sheath, swa or such like. However, it is possible to use the drop down list and choose the equivalent size. The NICEIC prefer the use of software for validation purposes. It takes the human mistake element out of certification. We have given up using it because it is pants. You can’t beat using your own judgment.
 
Very true and I agree. If you are using software such as Amtech then you would not be able to enter con, sheath, swa or such like. However, it is possible to use the drop down list and choose the equivalent size. The NICEIC prefer the use of software for validation purposes. It takes the human mistake element out of certification. We have given up using it because it is pants. You can’t beat using your own judgment.

Every report/certificate that we complete is computer generated but purely because it looks so good next to some hand scrawled competitor's report!

Also, it allows us to send reports/certificates as .pdf files.

We never use the validation part of the software, I cast my beady eye over every result!
 

Reply to Testing a Conduit Earting System in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
245
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
993
  • Question
It can also mean lasts or continues for two years.
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top