I have a homework question which I hope you will help me with. Heres the scenario.

I am called to inspect a 2 way CCU (in a garage for example) connected via SWA to the main CCU in the house. I notice there are banjo type connectors where the SWA joins the CCUs however there are no earth screws.

I install earth screws and fit fly leads to the earth bars at each CCU.

Question:
what is the correct procedure to test continuity of cpc at the 2 way CCU in the garage? I believe you could use r1+r2 for circuits fed from the secondary CCU but I assume you would also need to check the resistance between MET and secondary CCU earth bar ? Would it be a long lead method from MET to earth bar at secondary ccu? or am I missing something

Hope that makes sense.
 
I'd carry out a Ze (Zdb in this case) test, in the normal way, on the garage CU, which would prove continuity, or not.

The SWA feed to it, I classify as a cct belonging to the main CU, which would be tested when that CU is tested.
 
I'd carry out a Ze (Zdb in this case) test, in the normal way, on the garage CU, which would prove continuity, or not.

The SWA feed to it, I classify as a cct belonging to the main CU, which would be tested when that CU is tested.

I'm with Archy here, and the SWA is a "distribution circuit" not a final circuit, from the main CCU to your garage CCU, so depending on the protective device for that cable, you may have a different disconnection time. If it is protected by a 60898 mcb, then it is still 0.4 disconnection time, but if it is a fuse, it could be 5 seconds.

Cheers.............Howard
 
I'm assuming that they are referring to testing the cpc up to the CU in the garage.
I would isolate garage supply in the main CU, link Line and cpc in the garage, then test R1+R2 for that cable at the main CU. You can add this to your Ze to give your Zdb at the garage CU.
Of course, it could be done the other way round.
 
The more you read the question, the more ambiguous it gets. They don't make it easy sometimes, but it makes you think.
Trouble is they may give marks for one answer and not the other, quite valid, one.
 
I'm with Archy here, and the SWA is a "distribution circuit" not a final circuit... If it is protected by a 60898 mcb, then it is still 0.4 disconnection time, but if it is a fuse, it could be 5 seconds.

Can I ask you where it says this Howard.

I've always been led to believe that final circuits >32A and distribution circuits are 5 seconds (as per 411.3.2) regardless of the protective device.
 
I'm assuming that they are referring to testing the cpc up to the CU in the garage.
I would isolate garage supply in the main CU, link Line and cpc in the garage, then test R1+R2 for that cable at the main CU. You can add this to your Ze to give your Zdb at the garage CU.
Of course, it could be done the other way round.

Thanks for the replies, I think this is the answer I'm looking for. Unless anyone else has any different ideas?
 
Last edited:

Reply to Testing an additional ccu in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
832
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
930

Similar threads

Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
687
"When stoned..." Brilliant!
    • Like
Replies
6
Views
860

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top