testing at 400v domestic lighting in 2 too | on ElectriciansForums

Discuss testing at 400v domestic lighting in 2 too in the Domestic Electrician Forum area at ElectriciansForums.net

Joined
Aug 25, 2011
Messages
49
Reaction score
0
Location
South West London
Hi there
I was called out to a job this week where clients bulbs are blowing frequently. I expected to test voltage for the property and see a high voltage around 245/250...
However when I arrived the client told me a previous electrician, who I spoke to on the phone whilst I was there, had measured voltage at the switch for kitchen/living area at 380-400V.
He therefore disconnected the lights as they were just blowing straight away.

I told customer that I couldn't reconnect these lights as it would be dangerous. Electrician also said that sometimes there was power coming to the switch and other times it was dead. He said that he thought there may be a crossover between the flat above and this one ie. kitchen lights supplied by both a circuit from this flat and one from flat above.

I'm going back when the neighbour from the flat above is home so I can isolate her power and see if that affects my clients lights - has anyone ever come across anything like this before? And any thoughts why there would be 400v at lights in one particular room and not throughout the whole house?

I was getting 245v through rest of the flat.

Thanks! Kelly
 
As usual we need more information.

When you tested the kitchen switch,
What was the 400V measured between?
Was everything at 230V to earth?

If the single phase voltage is 245 you would normally expect phase - phase voltage to be over 415, being as low as 380V is a bit odd.
 
As above ^^ Eng54
Isolatote mains coming in and test for any voltage, if voltage is present at the switch then it is being fed from flat above!!
 
Does the building have 3phase to it...Flats on different phases?

Has anyone been doing stuff with either the lighting in the flat above or below, this other electrician he said he had ...curious why he was there and didn't sort it out!... some Electrician urh!!

I suspect the previous so called sparks has mixed the lighting in this flat with the lighting of the other flat maybe where they run together through ceiling/floorboards adjoining.

What was the other Electrician there for and did you ask why he hadn't sorted it?
 
If the building has 3-phase and your flat is fed by one of these phases then there could be a floating neutral. If it is floating it will assume a voltage approaching that of the heaviest loaded phase so you could test anything from 0 to 400 volts L-N depending on the overall building load characteristics. Be especially sure to make all your safe isolation tests because if you only test L-N it could catch you out.
 
Ahh, doh, sorry I missed the last line where he says ha got 245v in the rest of the flat. Depending on how he was testing the 400v at the lights and 245 v elsewhere it probably rules my theory out.
 
Sounds a bit dodgy,who knows what someone may have done,does the tenant know of any work that has been carried out recently in downstairs or upstairs flats? suspect anything and trust nothing would be my advice.Isolate downstairs and dead test(prove dead aswell) IR,continuity test etc,check to see if circuit is healthy,check supply voltage etc.
 
Hi there
I was called out to a job this week where clients bulbs are blowing frequently. I expected to test voltage for the property and see a high voltage around 245/250...
However when I arrived the client told me a previous electrician, who I spoke to on the phone whilst I was there, had measured voltage at the switch for kitchen/living area at 380-400V.
He therefore disconnected the lights as they were just blowing straight away.

I told customer that I couldn't reconnect these lights as it would be dangerous. Electrician also said that sometimes there was power coming to the switch and other times it was dead. He said that he thought there may be a crossover between the flat above and this one ie. kitchen lights supplied by both a circuit from this flat and one from flat above.

I'm going back when the neighbour from the flat above is home so I can isolate her power and see if that affects my clients lights - has anyone ever come across anything like this before? And any thoughts why there would be 400v at lights in one particular room and not throughout the whole house?

I was getting 245v through rest of the flat.

Thanks! Kelly

What voltage did you get on that circuit? Please don't tell me you didn't check for yourself.
 
Looks to be, yet another case of the disappearing OP!! Were all talking to ourselves again...lol!!

Bugger him then, How are you this morning Sir
 

Reply to testing at 400v domestic lighting in 2 too in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Question
I don't think it will work with only one stake unless some meters have different operating parameters. It doesn't necessarily have to be a stake...
Replies
3
Views
1K
People who claim to be plumbers... and tilers... New bath fitted and the drain is accessible from the side and there are isolating valves on the...
    • Like
Replies
0
Views
165
  • Question
By the looks of it the whole head comes off in one unit, guess it has a driver inside of it. Ive tried to Google the Image i have, one comes up...
Replies
3
Views
454
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
Replies
16
Views
2K
  • Question
I wish I took a photo now as I honestly can’t remember. All I know at the time I got results I was expecting but in hindsight I should have...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks