The Best Practice guidelines state from the ESC:
7.2. Planned change
7.2.1. The initial approach of the contractor planning the
replacement of a consumer unit should be to
encourage the customer to have a periodic
inspection and test of the installation carried out in
advance of the consumer unit being replaced.
7.2.2. If the customer refuses, a pre-work survey should be
carried out to ascertain if there are any immediate
or potential dangers, or any condition that would
cause unwanted tripping of an RCD, in the existing
installation affected by the change. As a minimum,
the survey should, include:
• making enquires with the user as to whether
there are any known defects, faults or damage,
• an internal visual inspection of the existing
consumer unit to determine, amongst other
things, the type and condition of the wiring
system used for the installation,
• an external visual inspection of other readily
accessible parts of the installation,
• a measurement of the external earth fault loop
impedance, Ze,
• a test of circuit protective conductor continuity
at the end of each final circuit, and
• an insulation resistance measurement of the
whole installation at the consumer unit, between
the live conductors connected together and the
protective conductor connected to the earthing
arrangement.
7.2.3. If any immediate danger, potential danger or
condition that would cause unwanted tripping of an
RCD is found, the customer should be informed that
remedial work is necessary to improve safety.
So it seems that the order of the day is to do as much inspecting and testing as you can before doing any work to assess the current condition of the installation. Have business terms about who pays for what, how and when. State what happens if unexpected faults are found after you have started work - who pays for them etc. Like another post stated, if yo have a copy of the Best Practice with you to back you up, it shows the customer you are a professional and not some numpty that looks at the old board and then says 'ÂŁ300 quid mate'
Personally I think it would be foolish to undertake a CU change without any pre-change investigative inspection and testing if you are a professional. qualified spark.
7.2. Planned change
7.2.1. The initial approach of the contractor planning the
replacement of a consumer unit should be to
encourage the customer to have a periodic
inspection and test of the installation carried out in
advance of the consumer unit being replaced.
7.2.2. If the customer refuses, a pre-work survey should be
carried out to ascertain if there are any immediate
or potential dangers, or any condition that would
cause unwanted tripping of an RCD, in the existing
installation affected by the change. As a minimum,
the survey should, include:
• making enquires with the user as to whether
there are any known defects, faults or damage,
• an internal visual inspection of the existing
consumer unit to determine, amongst other
things, the type and condition of the wiring
system used for the installation,
• an external visual inspection of other readily
accessible parts of the installation,
• a measurement of the external earth fault loop
impedance, Ze,
• a test of circuit protective conductor continuity
at the end of each final circuit, and
• an insulation resistance measurement of the
whole installation at the consumer unit, between
the live conductors connected together and the
protective conductor connected to the earthing
arrangement.
7.2.3. If any immediate danger, potential danger or
condition that would cause unwanted tripping of an
RCD is found, the customer should be informed that
remedial work is necessary to improve safety.
So it seems that the order of the day is to do as much inspecting and testing as you can before doing any work to assess the current condition of the installation. Have business terms about who pays for what, how and when. State what happens if unexpected faults are found after you have started work - who pays for them etc. Like another post stated, if yo have a copy of the Best Practice with you to back you up, it shows the customer you are a professional and not some numpty that looks at the old board and then says 'ÂŁ300 quid mate'
Personally I think it would be foolish to undertake a CU change without any pre-change investigative inspection and testing if you are a professional. qualified spark.