W

whazza22

When testing the insulation resistance on a s-plan heating system, do you need to disconnect all components or do you just disconnect the feed to programmer and test only between the d.b and feed?

Thanks
 
As long as you dont do a L-N IR test you wont do any damage....however if the boiler is a modern job with PCB's etc I would isolate that to be on the safe side.
 
This is my procedure for a full test on S or Y plan:

1. Isolate at FCU or lock off MCB.

2. Disconnect the load CPC from FCU. Using a long lead, measure R2 from this CPC to each point of the system (metal case of boiler, metal pump, metal motorised valve, and prog. and cyl. stat if these are metal)

3. At the wiring centre, disconnect the fixed wiring which is usually three of 3c+E, one to room stat and two to boiler/prog position. Megger these at 250V each core to earth, then put them back.

4. Visually inspect all flexes along their length.

5. Measure Zs at FCU, ensure it contains 3A fuse (5A if oil boiler). Re-energize the system and carry out a full functional test (boiler fires, motorised valve moves accross, pump spins).

6. Check bonding to gas (oil) and water incoming services. Ensure cross bonding is in place below boiler, if required by manufacturers instructions for gas appliance.

7. Finally, I always check that the radiator nearest the roomstat is fitted with a pair of lockshield valves. This is for compliance with building regs, not BS7671.

8. Note limitations on cert, record R2 and Zs, sign cert.
 

Reply to Testing Heating System in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Article
This is an RSS feed of thread: What are the best heating flushing systems Content of the thread: Any advice on selecting the best central heating...
Replies
0
Views
151

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top