Dave 85
Be honest here guys...When you do your testing, do you do it exactly the same as you would during a college assessment on every installation you work on/install
I dont, and I've never known a sparky who does
Feel free to accuse me of being a cowboy but here are the things I do different...
If im IR testing an old install and I get, say 50Mohms across the main Neutral/Phase and earth bars I'll write down every circuit as >200 rather than rip the fuseboard apart trying to find the circuit/circuits with less than 200. It doesn't really acheive anything IMO and takes time..
I never IR 500volts between L and N on an existing installation if the reading to earth is good, the risk of damaging the clients property is too great IMO
If im testing a new ring circuit installed by myself I'll test end to end on all 3 conductors but won't carry out cross connected ring continuity tests. On my own circuit I know its wired as a ring so this test is completely pointless.
On my own installations, if I know the chances of parallel paths etc are zero I sometimes gain my R1+R2 reading for a radial by testing Zs at the furthest point and deducting Ze. IMO this proves beyond all doubt you have a good R2. Now I know you're supposed to prove the circuits are compliant before energizing but we're all trying to make a living here and whats the worst that can happen when you know you do good connections every time and its all RCD'd
Also when I do a consumer unit change I do not test and inspect the installation to the same extent as I would an EICR. I just test ring end to end, IR L/N-E, RCD time, Ze and Zs at the end of each circuit-The going rate for C/U's (ÂŁ350) does not really allow for a whole day of testing and inspection and the house is gonna be 10 times safer than before I turned up anyway.
Hopefully this should arouse some fiery debate
Seems a bit of a case of common sense vs blindly following the rules you've been given without questioning the neccessity....
sorry my friend but the way u sound some1 will end up in hospital,
Yeah maybe me but I'm cool with that, I like to live life on the edge....nothing beats the adrenaline rush of changing a lightswitch faceplate live....
On a serious note please describe to me a realistic situation in which anything I've described would lead to someone (other than me) ending up in hospital....
You just said i do not do the full test,to me i think its wrong accident can happene later, after you leave the house when dave the builder come back home to have a shower..... then you said you make up the reading from 50ohms to 200 ohms.my q to you why not do the full test and put the true reading
My advise to anyone thinking of working live is dont do it,especially if its not necessary
Its a shame I dont follow that advise :blush5:
I would be scared witless by someone who never works live actually doing so
Historically,electricians work has always had working live as part and parcel of the job,it is such a big no no,because of the H+S culture that is now so much more evident than years gone by
I have the highest respect for the danger of electric shock, but it doesn't frighten me one little bit,
If you get a reading of 50Mohms when doing the global IR test then why not write 50Mohms in the box on the sheet? Its a pass! falsifying figures as you are is (a) wrong and (b) completely pointless in the circumstances above!
Reply to Testing...how far do you go? in the UK Electrical Forum area at ElectriciansForums.net
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested