Hi guys

ive not done any real testing on commercial jobs other than fault finding etc and was wondering, when dead testing lighting circuits would r1+r2 be accurate as the r2 will most probably not run the exact same route as the r1 with more connections etc so would you do an r2 flying lead method?

Thanks
 
Testing is testing really and circuits are circuits, just on a bigger scale.

Take a r1+r2 at every point, and dont forget to null your leads

You should look at completing a 2394/2395 course
 
So not just at the furthest point?

I sat my 2391 but failed the theory unfortunately and never got round to doing it again but will be doing the new course when I get time.
 
Well if you have not installed and are carrying out a periodic, you wont know which is the last connection or struggle to find the last connection, by testing every point you can record the highest reading you take and should clarify the end of the circuit
 
It's not just about getting a number to write in a box, the whole point is to prove the continuity of the cpc throughout the whole circuit. How many points do you think you need to test at to safely say that the cpc is present and correct at every point?
 
It's not just about getting a number to write in a box, the whole point is to prove the continuity of the cpc throughout the whole circuit. How many points do you think you need to test at to safely say that the cpc is present and correct at every point?

I fully understand the reason for testing the CPC and that we don't just test to fill numbers into box's, depending on how it's wired the EOL would prove its present at every point unless there are stabs off.

my question was more along the line of when using twin you know that the r2 is exactly the same length as the r1 but using singles they may differ so would you get a true reading?

cheers
 
I fully understand the reason for testing the CPC and that we don't just test to fill numbers into box's, depending on how it's wired the EOL would prove its present at every point unless there are stabs off.

my question was more along the line of when using twin you know that the r2 is exactly the same length as the r1 but using singles they may differ so would you get a true reading?

cheers
Hi,i am guessing you mean t&e?...if so,sometimes you will get readings which may indicate,through calculation,that the circuits are the same length,but this will not be so. Remember,you are just looking at on Ohms reading,and resistance can be made up of more than just the conductors impedance...:stooge_curly: This is why effective testing is achieved by more than just meter readings.
 
The reading you want to obtain is the resistance of the line and cpc in total, whether they are the same length or not is immaterial you will still need the resistance of that part of the earth loop path.

The readings may be lower if the cpc is connected to bonded metalwork along its route but this would still be the resistance of the cpc when in use and so is correct (assuming there are not faults on the circuit).
 
Hi guys

ive not done any real testing on commercial jobs other than fault finding etc and was wondering, when dead testing lighting circuits would r1+r2 be accurate as the r2 will most probably not run the exact same route as the r1 with more connections etc so would you do an r2 flying lead method?

Thanks

No I'm not going to say it, oh what the hell it's R1+R2 not r1+r2 signed pedant
 

Reply to Testing lighting in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
454
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
We just left it as it was, again the customer didn't seem too bothered, dont think she wanted me digging any further.
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top