Had another dispute with who i was working with today, with testing an new installation. Here goes
I always thought that the proper testing sequence is R1+R2, continuity of bonding, insulation resistance. Then ze, then zs. rcd
But the person i was working with today told me i should always test for insulation resistance before anything else. then do my r1 and r2 and then do an r1 + r2 to check the continuity of neutral, i've never heard of having to do this before but it doesn't seem a bad thing to do. but isn't the whole testing sequence designed to check that polarity is correct and you have an earth at the end of line. Therefore you don't have to check the neutral conductor, but on the ring you have to check the end to end of the neutral. but not on radials.
to me theres no point in doing the insulation resistance untill you know that everything has the correct polarity and there's no breaks in the circuit
I always thought that the proper testing sequence is R1+R2, continuity of bonding, insulation resistance. Then ze, then zs. rcd
But the person i was working with today told me i should always test for insulation resistance before anything else. then do my r1 and r2 and then do an r1 + r2 to check the continuity of neutral, i've never heard of having to do this before but it doesn't seem a bad thing to do. but isn't the whole testing sequence designed to check that polarity is correct and you have an earth at the end of line. Therefore you don't have to check the neutral conductor, but on the ring you have to check the end to end of the neutral. but not on radials.
to me theres no point in doing the insulation resistance untill you know that everything has the correct polarity and there's no breaks in the circuit