sid
you will find as you do more testing that the readings often vary a little from what you would expect its a case of learning what is an acceptable difference not every circ will be spot on by the book


Ok, I had done a test today on a ring main in a farm house.

I had readings between sockets from 0.28 to 0.36, this is obviously out of the allowed 0.05. Theres no spurs.

Would you say this is acceptable although its not "by the book" and happily record down your r1+r2 as 0.36 ?
 
Magic the 0.05 ohms figure is a rule of thumb i use before hunting its not in the book!!. As spread of figures is only 0.08 ohms of a difference then i would recon its ok. However its only going by figues you have given.
There are meny reasond for this spread of reading such worn contaacts if your usin a plug to take loops, Diffrences in connections if you are using probes.
As Jason,Mark has already said its experiance that will tell you these things and if you should go hunting. Thing to take into account are age,usage ect if its 6 year old building getting its first periodic i would say its fine no worries but if its a 50 year old building showing sighns of wear have a think. It could be corrosion in terminals have a GOOD hunt. On older buildings be carefull!!
 
Cheers for your replys.. appreciate it..

Also i cant find max Ze for different earthing arangements in the red book.. anyone point me in the right direction?
 
TNCS - 0.35
TNS - 0.8
TT - 1667 although 200 is acceptable but it could be unstable and so should ideally be under 100.

Page 11 OSG
 
Last edited by a moderator:
TNCS - 0.35
TNS - 0.8
TT - 1667 although 200 is acceptable but it could be unstable and so should ideally be under 100.

Page 11 OSG


Cheers J

I've measured Ze on a TT as 0.27

Would you say ive messed up somewhere on the test as this seems VERY low ???
 
Cheers J

I've measured Ze on a TT as 0.27

Would you say ive messed up somewhere on the test as this seems VERY low ???

If you positively isolated the Main Earthing conductor from the Earth bar and main bonds then you will probably be reading through a parrallel path close to your earth rod...maybe a water or gas pipe....if this is your reading then record it on your test sheet but note down your reason.
 

Reply to Testing.. Never goes right.. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top