All sockets where checked and they looked fine but then ran out of time so back in tues for further investigation. Did try another rcbo an still the same.
 
I would dead test the cct and test every point with the figure of 8 method (again) IMO something has been connected up incorrectly. I don't use a 1700 series Megger but surely the tester is pointing to a connection issue and plugging something in the RCD is seeing the fault!
 
Are you plugging tester into same socket as appliance when it trips? could be socket is down (faulty socket) test between l-n n-e e-l on the socket see if it belles out.
another thing ive been to job where rcd is tripping and IR test at board is showing me fault between live and cpc. when ive taken off the first socket on the ring and retested the fault has cleared. this was down to the cables being squashed but not enough to break the insulation but thinning the insulation enough for it to freakishly show a fault between the line conductor and the earthed metal backbox!

Just a couple of ideas!

J
 
Sounds like........L is in N,..... N is in E........at the socket you are testing from or a full reversed polarity on the circuit and a neutral to earth fault.
 

Reply to testing novice in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

I don’t see an rcd here. Is it elsewhere, supplying this board? It looks like it’s in a garage… is there excessive moisture getting into...
Replies
7
Views
1K
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top