J

james86

I have been asked to test an offpeak cdu but what am I to do with the live tests? Do I calculate using them using ze from on peak cdu? Or do I go back at night!? Lol. Also what about schedule of inspection for functional tests??? Cheers
 
you hang around till the power comes on at 12am!!!

alternatively you LIM the live tests and calculate ZS from R1R2 + ZE (main incomer on live side)

you also LIM the functionaal tests or you disconnect and put you continuity meter either side of the switch!!
 
Yes, you do as Durham suggests or you energise (safely) the off-peak board from the 24-hour supply for the purpose of live testing.

If this is a periodic inspection then I'd go with Durham, initial verification and I just have to see everything working!
 
Firstly. Yes it is pir, confusion set in because client had spark who refused to test that board because of the off peak nature!

Secondly. Thanks for that, never thought of doing functional test like that on a storage. Won't the element just give continuity thow ????
 
Firstly. Yes it is pir, confusion set in because client had spark who refused to test that board because of the off peak nature!

Secondly. Thanks for that, never thought of doing functional test like that on a storage. Won't the element just give continuity thow ????

You will get a resistance reading through the element(s) but you'll also be able to check the switching of the input thermostat controls.(assuming storage heating)
 
Last edited:
Cheers guys, I think in order to energise it would involve breaking seal on storm fuse because there is no isolator!? I know what u mean though about seeing everything working. I got to say this forum is the best thing since sliced bread, I am getting loads of answers! Once again many thanks chaps
 
Cheers guys, I think in order to energise it would involve breaking seal on storm fuse because there is no isolator!? I know what u mean though about seeing everything working. I got to say this forum is the best thing since sliced bread, I am getting loads of answers! Once again many thanks chaps

It is a great forum, don't forget the 'thanks button' ;)
 

Reply to testing off peak consumer unit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

If two tariffs are sufficient, and you don't need too many ways, you can easily add an SPD kit to the Fusebox F2014DT dual tariff board. The only...
Replies
1
Views
302
  • Question
Part III:). I think I have clarity-having spoken to my electrician who installed my heaters, he said that the part of my fuseboard that is...
2 3 4
Replies
52
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top