You start with the basic information and I would probably prefer you to make some information so that you will recognize what is the function of that certain matter and how does it affect. However, please make some clarification regarding this matter.



It seems our American friend is trying to learn about the electrical trade and is doing so through a second language
He seems to be requesting a better description of the supply type etc to help him understand what is being discussed

Or
They are screening Yes minister in LA
 
Hello All,

I have delved further into this and have done a ZE test at the hook up point and got a reading of 3.1 ohms which is still above the 0.8 max it should be. I then tested inside the caravan at the ccu and got somewhere around 40 ohms. It stands to reason that I have a dodgy connection between the ccu and hook up point which I will fix by reterminating at the hook up point and retesting at the ccu hopefully with better results, if not then I will run in a new supply.

Thanks all, hope you can understand this as I did not understand the last post by a person from abroad.

Cheers, Allan.
 
Hello All,

I have delved further into this and have done a ZE test at the hook up point and got a reading of 3.1 ohms which is still above the 0.8 max it should be. I then tested inside the caravan at the ccu and got somewhere around 40 ohms. It stands to reason that I have a dodgy connection between the ccu and hook up point which I will fix by reterminating at the hook up point and retesting at the ccu hopefully with better results, if not then I will run in a new supply.

Thanks all, hope you can understand this as I did not understand the last post by a person from abroad.

Cheers, Allan.

So what about the Ze value at the source where this hook-up point (and all the rest of the hook-up points on the site) are fed from?? This is where you should have started your investigation, not at the adjacent hook-up point to the caravan your working on!! The 3.1 ohm Zdb value at this hook-up still doesn't comply does with a TN-S system does it?? You will at the very least need to inform the caravan site owner operator/management of your findings. My best guess at the moment (if it is a TN-S system) would be a combination of long cable distances and the SWA earthing connections/continuity at the hook-up positions...
 
Sink a rod & tt the pitch supply box & check for dodgy connections on the. Socket outlet & flex to van.
Don't change any rcd's as that's how it's supposed to be wired
Also check out section 708 & 721 in the regs
Cheers
 
Well, well, ...In other words don't bother being an electrician and checking anything, just bung a rod in the ground and TT the pitch!! Makes perfect sense that, 200 ohms to replace 3 ohms!! Oh and who cares, if that there won't be any discrimination between the supply hook-up and caravan RCDs!!

Great advise all round that!! ...Jesus!!
 
Well he's obviously got some problems there regarding the supply earth, or the distribution to the pitch. Obviously getting a good reading on the tns earth would be a better solution than a rod.

Well, well, ...In other words don't bother being an electrician and checking anything, just bung a rod in the ground and TT the pitch!! Makes perfect sense that, 200 ohms to replace 3 ohms!! Oh and who cares, if that there won't be any discrimination between the supply hook-up and caravan RCDs!!

Great advise all round that!! ...Jesus!!

Also you should check 708 & 721 in the regs as they don't call for discrimination between the pitch & van rcds & insist on 30mA devices at each location.
 
Ze first test u ever do before carrying out any work minor or major, you shouldn't really be adding to an installation that isn't earthed correctly, like you say your new to testing so you will learn from this
 
Well he's obviously got some problems there regarding the supply earth, or the distribution to the pitch. Obviously getting a good reading on the tns earth would be a better solution than a rod.



Also you should check 708 & 721 in the regs as they don't call for discrimination between the pitch & van rcds & insist on 30mA devices at each location.

Yet another load of nonsense from the BGB then!! I'm sure that a static caravan owner/resident will fully appreciate having to go outside, braving torrential rain or a snow blizzard to reset an RCD!! lol!!
 

Reply to Testing question. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
597
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

  • Question
Thank you so much for that! When I went to do the Ze at the DB, I tripped the RCD in the CU in the house, I understand that's a hard question...
Replies
2
Views
244
  • Question
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...
Replies
10
Views
657

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top