testing RCD at Consumer unit | on ElectriciansForums

Discuss testing RCD at Consumer unit in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jan 21, 2011
Messages
581
Reaction score
34
hi guys

now i usually test RCD,s via the nearest plug socket as i feel it is a much safer and easier way to carry out a live test .

But just been reading GN3 and it states that they should be tested on the actual load side of the RCD with all loads disconnected. im assuming this means to test between the output terminals L/N of the RCD and the earth bar with all Mcb's off and main switch on. or have i got it wrong and the mcb's have to be on and circuits under no load???

and also i am correct in thinking only one test is needed for all circuits covered by the RCD not individual rcd test for each circuit
??

many thanks
 
yea the regs do state, to be done at the CCU. I questioned this myself as it is easy with the plug addapt of most multi funct testers, just to do a auto test. but having said that if your doing a full board with multiple circuits then its quicker to do one test (per RCD) at the board.
Also your readings might be slightly off testing remote from the board, due to other influences.
 
i usually do it the easy way, all loads unplugged and auto test at a socket close to the CU. testing at the RCD may be recommended, but iy's too easy for a lead to slip contact while you're resetting the RCD. test aborted.
 
Last edited:
yes i guess it might be quicker as your at the C.U. for both rcds and saves walking back to the C,U. to reset, just seems safer to use a socket outlet that is covered by each RCD than working on a live board especially with main switch on. but your right the regs do state the test should be done at the C.U.and any other influences should be omitted.
 
I understand that the RCD test is testing the functionality of the RCD itself, and not the circuit, but what Murdoch says makes sense to my small brain, ensuring the RCD trips within limits at the extremity of the circuit.
 
I understand that the RCD test is testing the functionality of the RCD itself, and not the circuit, but what Murdoch says makes sense to my small brain, ensuring the RCD trips within limits at the extremity of the circuit.
That's what your max Zs values are there for, to prove that the device will operate at the extremity of the circuit. Your proving that the device conforms to spec on disconnect times. Otherwise you'd have to test at the extremity of all circuits protected by the RCD.
 

Reply to testing RCD at Consumer unit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
685

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top