hi guys
now i usually test RCD,s via the nearest plug socket as i feel it is a much safer and easier way to carry out a live test .
But just been reading GN3 and it states that they should be tested on the actual load side of the RCD with all loads disconnected. im assuming this means to test between the output terminals L/N of the RCD and the earth bar with all Mcb's off and main switch on. or have i got it wrong and the mcb's have to be on and circuits under no load???
and also i am correct in thinking only one test is needed for all circuits covered by the RCD not individual rcd test for each circuit
??
many thanks
now i usually test RCD,s via the nearest plug socket as i feel it is a much safer and easier way to carry out a live test .
But just been reading GN3 and it states that they should be tested on the actual load side of the RCD with all loads disconnected. im assuming this means to test between the output terminals L/N of the RCD and the earth bar with all Mcb's off and main switch on. or have i got it wrong and the mcb's have to be on and circuits under no load???