When I first went to job I thought it had to ring circuits as there was 2 30amp fuse in board I opened board and see 1 ring 30amp fuse 2.5 mm t&e if it is a ring and there is a break somewhere in the middle and I can't access it to repair it can I do it as 2 radials would this work and comply
with the regs in the UK. i dont know
if it was a US. you would have to run another neutral!
regardless you need to sort it out
if it was a ring and is broken some place you need to find out where and terminate it properly.
if its 2 radials you should install separate breakers
 
As it has been said before disconnect at the CU (all conductors relating to that circuit) disconnect all the socket outs and do a continuity test, this will enable you to if it is two radials joined at the CU, or you have a broken ring, basic stuff really
 
Hi
It sounds like you have two radials there, but there may be another explanation for it.
is it possible that the ring circuit has been connected into two separate breakers accidentally. if you turn off the breaker for this ring circuit and check to see if any sockets are still live.
It sounds odd but I have come across this a couple of times.
 
Hi
It sounds like you have two radials there, but there may be another explanation for it.
is it possible that the ring circuit has been connected into two separate breakers accidentally. if you turn off the breaker for this ring circuit and check to see if any sockets are still live.
It sounds odd but I have come across this a couple of times.
Read the ops post this is not the case :)
 
So connect 1 of the ends of the "ring" to an MCB and go around and see what is now live and mark on the sketch of the site you made before you started. Then do the same with the "other" end......
 
Since when has it not been 'legal' to have two radials on one breaker/fuse? If it's done right it's perfectly acceptable..... Classic newbie mistake to see two cables going into a breaker and assume it's a ring, often it is not. If there is no continuity between the cables then it's not a ring.....next job is to check that it wasn't supposed to be a ring at some point in the past and to ensure that the breaker/fuse is appropriately rated.
 
I have found a situation where the ring and a separate radial had been mixed up between 2 breakers. So one leg of the ring and radial in 1 MCB, and the other leg of the ring in another MCB. Not very likely but it's a possible scenario.
 
Since when has it not been 'legal' to have two radials on one breaker/fuse? If it's done right it's perfectly acceptable..... Classic newbie mistake to see two cables going into a breaker and assume it's a ring, often it is not.

You can also have a spur at the origin, i.e. at the fuse/circuit breaker.
 
Can someone explain what all this crap about 'legal' or 'against the regs' or 'illegal' is supposed to mean? Is it that something doesn't comply with a non statutory Regulation or perhaps is a deviation ?
 
It's crap to refer to something as not being legal just because someone believes (as it happens wrongly) that something doesn't comply with BS7671.
 
Can someone explain what all this crap about 'legal' or 'against the regs' or 'illegal' is supposed to mean? Is it that something doesn't comply with a non statutory Regulation or perhaps is a deviation ?

it wasnt intended to alarm anyone
as i stated i dont know about UK regs but is some zones in the US you cannot have more than one conductor on a breaker unless its designed for it, even then it may fail an inspection.

what i was saying is that it sounds like 2 radials under 1 breaker and needs to be sorted out regardless (at least for the OP'S peace of mind)
 
Our breakers can take more than one conductor, after all we use ring final circuits often enough! And there is nothing preventing you having more than one branch on a radial circuit originating at the breaker either. On a ring you could even have a spur starting at the distribution board, so you'd have three conductors in the breaker. I'm not saying I would do this but as far as the regs go, it's fine.
 
Our breakers can take more than one conductor, after all we use ring final circuits often enough! And there is nothing preventing you having more than one branch on a radial circuit originating at the breaker either. On a ring you could even have a spur starting at the distribution board, so you'd have three conductors in the breaker. I'm not saying I would do this but as far as the regs go, it's fine.

Reg 314 Covers division of circuits in an Installation you could apply this reg to multiple circuit in one MCB but would only give it a code 3 if you wanted to be really fussy, The Op should take a look at this REG
 

Reply to Testing ring circuit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
559
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
925

Similar threads

Well we called it a room, but it was only a hole in the ground covered with bit of canvas.
Replies
13
Views
762
Who knows? There's this, in the OSG app H: "Permanently connected equipment should be locally protected by a fuse complying with BS 1362 of...
Replies
3
Views
279

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top