B

Bonse

Hi People

So im testing my ring rinal circuit....

i do my end to end test.....

I join incoming CPC to outgoing Line and vice versa......

I then go around my circuit with my tester noting the readings at each socket and record the highest reading.....


Ok so this is my R1+R2 = 0.3

My measured Ze is 0.17Ohms

So my Zs = 0.29 + 0.17

Zs calculated is = 0.46....


Ok so now i reconnect the line and earth in the terminals and liven up my circuit (I have already done the insulation resistance also sorry didnt mention)

Then i goto the socket i got the highest R1+R2 at and do my Zs....


I get a result of 0.31Ohms

Can anyone explain how this is possible?

If Zs= Ze + (R1+R2)

How can i get such different results between calculated and measured?????


Spoke to my friend who has been around a long time and he tells me he does his R1+R2 at the consumer unit.... even though in the OSG it says the way i did it was correct.

When i do it his way i get slightly different readings but they still do not work out in the end....

The circuit is otherwise sound.

Im really looking forward to the replies, oh and yes the leads were nulled


Darren
 
Im with you on this..... if i disconnect the main bonding and retest? theres nothing plugged in within the circuit either

What are you trying to achieve though, parallel paths are fine!

Even in a simple 'insulated' domestic installation, you have parallel paths everywhere from protective bonding to boiler connections etc. etc.
 
Last edited:
Im simply testing the equation Zs = Ze + (R1+R2)

and understanding why i can get different measured results to calculated

I do understand the drill just this was niggling me a bit
 
Im with you on this..... if i disconnect the main bonding and retest? theres nothing plugged in within the circuit either

Hope you don't mean Zs testing after removing a protective conductor. This should never be done.

Measured Zs is always expected to be lower than Ze + R1 + R2 due to the parallel paths connected to the MET whilst Zs testing.
 

Reply to Testing Ring final circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top