I said bonding not main protective Conductor

thanks for the input like i said i just wanted to get the result as calculated. as a lot of sparks will calculate and be happy with the result
 
basically the answer is parallel paths....

The fact that the Zs is lower than Ze + (R1+R2) is fine on the test certificate.

Thanks everyone much appreciated!
 
basically the answer is parallel paths....

The fact that the Zs is lower than Ze + (R1+R2) is fine on the test certificate.

Thanks everyone much appreciated!

That's about it, a competent person reading the test results would expect that scenario.
 
That's about it, a competent person reading the test results would expect that scenario.

Correct, and in actual fact if the Measured Zs recorded on the SOTR was equal to the recorded Ze plus the recorded R1 + R2 then a competent person checking your results would be very suspicious of your R1 + R2 readings. He would probably suspect that they weren't resistance readings at all. ;0)
 
Correct, and in actual fact if the Measured Zs recorded on the SOTR was equal to the recorded Ze plus the recorded R1 + R2 then a competent person checking your results would be very suspicious of your R1 + R2 readings. He would probably suspect that they weren't resistance readings at all. ;0)

Lol, but do remember that in accordance with Guidance Note 3, calculation of Zs from Ze+(R1+R2) is acceptable
 
So to eliminate parallel paths a calculations probably better, or do both and if he measured result is less than the calculated it can be down to parallel paths whith is acceptable

All good stuff guys!

Be reading GN3 again!
 

Reply to Testing Ring final circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top