Hi currently at college doing level 3 testing and inspection just a few questions if anyone can help

For the Ring circuit it is all wired in 2.5 singles and has one spur off the the ring
After doing end to end tests is the calculation r1/2 seen as though the cables are the same size?
Also if there is a spur and is the highest reading do i write this down for the R1+R2 of the ring circuit Thanks
 
VerIfy the R1&R2 readings from the spur, but record the highest reading obtained on the ring. If the spurs reading is very high due to length of cable etc then it may be worth recording also.
 
Imo the spur is part of the circuit hence if thats the highest reading that goes in the box Miss read Op Im meaning Zs
 
Last edited by a moderator:
So when i am checking the R1+R2 do i add r1+r2/4 or r1/2 as all the conductors are wired in 2.5mm2 singles Thanks again
 
So when i am checking the R1+R2 do i add r1+r2/4 or r1/2 as all the conductors are wired in 2.5mm2 singles Thanks again

Hi mate,

You can do it either way - you'll get the same answer.

Don't forget, this calculation is just to give you an idea of the reading to expect when you actually measure R1 + R2.
 

Reply to Testing ring main with a spur in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top