Similar to what Malcom pointed out, Earth is paramount, get yourself a long lead and test the chassis remembering the touch voltage (50V).
In most cases the Zs and Zdc readings at hook-ups and within caravans can be extremley high. If the Park manager is reluctant to spend on upgrading earthing at hook-up etc....just write an addtional report highlighting the dangers and send it the owner along with EICR.
Solution:
It would mean re-glanding at a number of hook-ups if it's a TNS system with SWA or running a separate earth cable. In some cases it might be re-newing a roofer bolt and nut.
If you are unable upgrade earth, would it be worth installing a rod to get the reading down in spite of the regs stipulating that 2 x earth systems shouldn't be mixed?