Correct me if I am wrong but if we are to test a SELV transformer do we:

1. Join conductors of low voltage side of transformer together.
2. Join conductors of primary side of transformer together.
3. Test between these at a voltage of 500V look for minimum reading of 1 MOhm.
4. Test between joined conductors of low voltage side and the earth of the primary side at 500V Look for minimum of 1MOhm.
5. Test between conductors of low voltage side at 250V look for minimum reading of 0.5 MOhm.

When testing the conductors on the low voltage side at 250V this is including the transformer winding right?
I mean is this low 250V test a test of insulation resistance of cables but also including the resistance of the winding inside the transformer.
Is that right?
Thanks.
 
I mean when testing the SELV circuit for insulation resistance do we simply connect our IR tester to the two conductors of the SELV circuit and wack 250V down them and hope for a reading of 0.5MOhm or is there something I am missing here?
It seems to me that if this is the method of testing then all we are really testing is the resistance of the winding of the transformer.
 
Correct me if I am wrong but if we are to test a SELV transformer do we:

1. Join conductors of low voltage side of transformer together.
2. Join conductors of primary side of transformer together.
3. Test between these at a voltage of 500V look for minimum reading of 1 MOhm.
4. Test between joined conductors of low voltage side and the earth of the primary side at 500V Look for minimum of 1MOhm.
5. Test between conductors of low voltage side at 250V look for minimum reading of 0.5 MOhm.

When testing the conductors on the low voltage side at 250V this is including the transformer winding right?
I mean is this low 250V test a test of insulation resistance of cables but also including the resistance of the winding inside the transformer.
Is that right?
Thanks.

Pretty much spot on but once you've done the primary/secondary tests, there's no need to do the 250 V tests with the secondary included.
 
Thanks for the answers.
The thing that really confuses me is that in GN3 and other publications it says to test SELV at 250v DC but no where does it say to disconnect the transformer.
I have not read this anywhere and I have been reading a lot.
I mean are we supposed to disconnect the transformer and IR test the low voltage side at 250V or are we supposed to IR test the low voltage side at 250V with the transformer in place.
The transformer does not seem to be mentioned in any publication.
Just as a second question, what would the resistance of the transformer winding be if we did a continuity test on it?
The low voltage side I mean.
Thanks.
 
Last edited:
1. i never IR test the secondary. 2. if you were to measure the winding resistance, the secondary reading would be approx. 1/20 of the primary. the reading though would only be resistive though. no account taken of the inductance, unless you have an LCR meter.
 
Can you see the confusion though.
GN3 says to test SELV circuits at 250V DC but does not mention if we are to disconnect the transformer or not.
And no other publication mentions it either.
Well none that I have read.
I mean what exactly are we IR testing at 250V?
Is it the resistance between the two live conductors of the supply side?
 
Last edited:
I wouldn't even consider a transformer test to be neccessary if it could be confirmed by inspection that the transformer complied with BS EN 61558-2-6 or BS EN 60742 or BS 3535-1 for older products.

Other suitable sources for SELV should meet the requirements set out in BS 7671:2008.
 
I wouldn't even consider a transformer test to be neccessary if it could be confirmed by inspection that the transformer complied with BS EN 61558-2-6 or BS EN 60742 or BS 3535-1 for older products.

Other suitable sources for SELV should meet the requirements set out in BS 7671:2008.

Just curious, why wouldn't you even consider a transformer test on a SELV TX?? A BS number only gives the TX a build configuration standard. All TX's have a BS number, it hasn't to my knowledge negated them from being subjected to electrical testing as and when required...
 
:detective:

The test procedure says test between the SELV conductors at 250V.
Minimum insulation resistance reading 0.5 MOhms.

This also brings us onto the subject of isolating transformers.
Testing the isolated circuit insulation resistance.
I guess a SELV circuit is a small version of an earth free equipotential zone.
That must be the answer.
The difference is it is at a voltage of less than 50V.
The only concern about insulation resistance would be a short circuit not a fault to earth.
The important thing being to have an appropriate over current device, I guess that's the heat sensor in the transformer.
The appropriate BS reading would tell us the transformer had been tested for overload much the same as a BS number for an MCB.

I wonder if that is why the reading is only 0.5 MOhms between conductors.

But I still don't know if I am to test insulation resistance at 250V with the transformer in circuit or not.
I'll get there in the end.

:euro:
 
Last edited:
This is definitely related to this topic but slightly different. I have a shaver socket integrated with a mirror light with pull cord switch; obviously the shaver socket is SELV. How do I test the SELV part of the equipment in this case? Cheers!
 
Just curious, why wouldn't you even consider a transformer test on a SELV TX?? A BS number only gives the TX a build configuration standard. All TX's have a BS number, it hasn't to my knowledge negated them from being subjected to electrical testing as and when required...

In general, the requirement is a thorough inspection to make sure that the source of low voltage (usually a safety isolating transformer) complies in all respects with the British Standard concerned, followed by an insulation test between the extra-low voltage and low voltage systems.

Guidance Note 3 (page 40) reads:

The source of the SELV supply should be inspected for conformity with regulation 414.3 and if necessary the voltage should be measured to confirm that it does not exceed 50 V ac or 120 V dc.
 
This is definitely related to this topic but slightly different. I have a shaver socket integrated with a mirror light with pull cord switch; obviously the shaver socket is SELV. How do I test the SELV part of the equipment in this case? Cheers!

The shaver is not SELV it is electrically isolated from the rest of the installation so the tests you would do would be to make sure the voltage levels are correct with a volt meter connected between live conductors of the electrically separated circuit and also test for electrical separation this would mean isolating the circuit supplying the transformer, joining conductors of the primary side together, joining the conductors of the secondary side together and then testing between both sets of conductors (IR test) at 500V.
Also test between the joined conductors of the secondary (isolated side) side and earth of the primary side at 500V.

Minimum insulation resistance value 1MOhm.
 
Last edited:
In general, the requirement is a thorough inspection to make sure that the source of low voltage (usually a safety isolating transformer) complies in all respects with the British Standard concerned, followed by an insulation test between the extra-low voltage and low voltage systems.

Guidance Note 3 (page 40) reads:

The source of the SELV supply should be inspected for conformity with regulation 414.3 and if necessary the voltage should be measured to confirm that it does not exceed 50 V ac or 120 V dc.


So you would undertake electrical testing on a SELV TX... I was just curious!! I as a matter of course would always check between primary-secondary, and primary - earth/secondary-earth

Had plenty of main contractors complain about testing Distribution TXs in the past, as they always come with a full test report etc, from the factory. They never seem to understand that lot's can happen to a large heavy TX during transportation, often involving sea voyages. Found more than just a couple that needed factory technicians to undertake warranty work at site...
 
So you would undertake electrical testing on a SELV TX... I was just curious!! I as a matter of course would always check between primary-secondary, and primary - earth/secondary-earth

Had plenty of main contractors complain about testing Distribution TXs in the past, as they always come with a full test report etc, from the factory. They never seem to understand that lot's can happen to a large heavy TX during transportation, often involving sea voyages. Found more than just a couple that needed factory technicians to undertake warranty work at site...

And the forklift or crane for final positioning!

It's competent judgement really, I wouldn't expect anyone to start testing the transformers on a small SELV lighting system but on larger projects I'd find it harder to justify not carrying out the transformer tests.
 
And the forklift or crane for final positioning!

It's competent judgement really, I wouldn't expect anyone to start testing the transformers on a small SELV lighting system but on larger projects I'd find it harder to justify not carrying out the transformer tests.

11kv/12v get some lights on that baby .........................
 
And the forklift or crane for final positioning!

It's competent judgement really, I wouldn't expect anyone to start testing the transformers on a small SELV lighting system but on larger projects I'd find it harder to justify not carrying out the transformer tests.


If you were to see how they treat some of the containers at the docks, and the positioning of them on the decks of those container ships, that forklift for final positioning would be the least of your worries .... lol!!!!

Had at least two TXs with cracked tanks, bad enough to be letting oil pass, bent and/or punctured cooling fins, Welded pipe work for expansion tanks sheared off, Pressure relief valves bent, buckled, and leaking. HV ceramic bushings, cracked/broken, LV bus bars and casing bent an buckled.... Having said all that, the vast majority arrive on site in pretty good condition..:rofl:
 
Right I have at last got an answer for this question.
As regards the insulation resistance testing of SELV conductors at 250V with minimum allowable value of 0.5MOhms.
Quote:

This test is intended for when you have say a large torrodial transformer feeding dozens of lights with a significant amount of cabling. The transformer and all the lamps would have to be taken out of circuit before the test is done.
It is very rarely used as common practise is to now use pre-leaded transformers which connect directly to the lampholder of a single light fitting.
For a 2391 exam, you need to know how it would be done, but you will never have to do it in this instance. You may however come across some low voltage- selv heating/logic/building controls which are in this category at some time.
 
I am really glad I don't need to investigate testing procedures for SELV,Electrical separation for months on end.
Amongst all the posts,not one post regards multimeter internal resistance in relation to measuring SELV, El circuit output voltages.secondary side as incompatible meter will not indicate correct voltage say these levels
Anytime much ado about nothing measuring toroidal txs resistances,secondary voltages etc load of nonsense
Only time you would consider measuring this type of equipment would be fault finding absolutely nothing to do with EICR,except to say final circuit not working investigation required..
If I buy a kettle I don't measure the element resistance to see if it meets standards indicated on relevant docs standards codes etc I fill it with water switch on and see.
Anyhow the regs for testing in line with your own experience are more than adequate to determine compliance.
Don't try to complicate matters about something you are really not trained/educated to analyse.
Have a safe working day.
 

Reply to Testing the SELV in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

out of interest UK, how do you know what kit is connected?
Replies
8
Views
922
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
Replies
24
Views
3K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
Replies
20
Views
1K
  • Question
Second Update: 12/25/2023 Hey everyone, so I solved my doorbell issue. Turns out there were two reasons why my doorbell wasn't turning on. 1.)...
Replies
5
Views
2K
When working in the motor repairs industry you have to fill in test sheets and keep them for so long. Doing that will do is ok for most things but...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks