That's true and of course if you were in a classroom situation then it's not what you do. But by will get a decent indication if there is a problem or not. If you measure at the source and get one voltage and there is a big difference at the load end, then you can be pretty sure you have a problem
When you calculate the volt drop you use the design current of the circuit, so surely you'd have to have your circuit pulling its full design current to measure the volt drop properly
Reply to Testing volt drop in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
I'd always go for 25mm2 5core over 50mm2 3core, with the cores paired up. Considerably cheaper, easier to terminate and ready to go, if ever 3...