Your PFC is going to be the highest Line to Neutral reading multiplied by 1.732, or doubled to be on the "safe side".
Or measured directly line-line.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Testing ze at the origin in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Your PFC is going to be the highest Line to Neutral reading multiplied by 1.732, or doubled to be on the "safe side".
Or measured directly line-line.
Yeah as long as the tester is suitable to measure across Lines.
You might want to rethink using a PEFC value gained during the Ze test.
Why would you want to rethink? Are you referring to the fact that the fault current under short-circuit conditions in a 3-ph system is significantly higher than the line-earth fault current?
Why would you want to rethink? Are you referring to the fact that the fault current under short-circuit conditions in a 3-ph system is significantly higher than the line-earth fault current?
No mate, it is because PEFC is taken with all bonding conductors and CPCs connected, Ze is taken with the Earthing conductor disconnected from the rest and measured on it's own.
PSSC is a different measurement.
No mate, it is because PEFC is taken with all bonding conductors and CPCs connected, Ze is taken with the Earthing conductor disconnected from the rest and measured on it's own.
PSSC is a different measurement.