Discuss Testing Zs at Lighting switch's with no neutral in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

DanBrown

Could anyone just give me a bit of advice regarding a Zs test at a light switch, as the tester i have just baught is the ''Fluke 1653'' tester and it uses a 3 wire test earth, live, neutral to aquire the Zs.

Am i right in saying that you have to do it manually by shorting live / earth at C/U and do a ohms check then add this to your Ze test?.

Your thaughts would be appreciated, Thanks
 
Last edited by a moderator:
Dan

connect line (used to be called phase) to earth bar at the cu (supply isolated obviuosly!)

and measure between line and cpc at the light switch on low resistance ohms. This is your (R1+R2) value, and when added to the Ze is your ZS. Its very unlikely this will be recorded on your schedule of test results, as the highest Zs value should be a the switched live conductor on the last light in the circuit.

If you measure Zs at the switch, you are (in theory) contravening the Electricity at Work Regulations
 
In response to your anwer ian.
What do you actually mean by saying put neutral to earth to make the tester work.
Thanks anyway
 
Last edited by a moderator:
I agree with Easyfox

i would just confirm R2 at the light switch, and do my Zs at the ceiling rose (calaculated from the (R1+R2) value

Dan, i use a Megger. If we are on 'no trip loop' we use three leads, and normal earth fault loop is two leads (which connect to line and cpc). Cant recall how the Fluke carries out the Zs or Ze test, but do you have a two or three lead option? it wont be called 'no trip loop' but somenthing similar
 
Hi Guys,
Thanks for all your responses, The only reason i asked about testing at a light switch is to double check and make sure that the maximum Zs i recorded was actually the maximum Zs, seem s a bit stupid on my behalf but im kinda new to testing my work off. I am aware that with the theory and the actual Zs should be at the furthest part of the circuit as this has the highest resistance reading. Just wanted to 100% check and make sure my reading's were correct.

In response to you previous question tony, the tester uses 3 wire only, and it has ''non trip'', when you dis-connect the neutral lead from the tester it says ''lead''. You must be right in saying put neutral + earth leads onto earth terminal and live to live. I'll give it a try....

Thanks Guys
 
All the leads in rotary sw to Z Tester should be on L-PE

At light put green crock to earth, blue to neutral and then red to phase.
 
For loop testing with the Fluke, choosing L-PE will do a low current "no trip" 3 wire test. Choosing L-P will do a high current 2 wire test. For this connect the L probe to live and N to earth. Remember that the 2 wire test will trip any RCDs.
 
so the Fluke IS the same as the Megger

thought it would be

also think that two lead test will be virtually redundant under the 17th, all except PFC's at the CU
 
Hi
R1+R2 is only available at light drop / ceiling rose (also much easier to do).

Switch off main switch. Temp short MCB live to earth. at furthest rose, test using two leads (as L & E available).

Record result and remove temp link.

As shown on page 217/218 NICEIC Inspection, Testing, Certification and Reporting.

Hi

Also if you want to include switch drop, still test at ceiling rose with light switch on. Use Switch live, Neutral and earth. Then you get longest path of Live.
 
Last edited by a moderator:
Hi
R1+R2 is only available at light drop / ceiling rose (also much easier to do).

Switch off main switch. Temp short MCB live to earth. at furthest rose, test using two or three leads (as L, N & E available).

Record result and remove temp link.

As shown on page 217/218 NICEIC Inspection, Testing, Certification and Reporting.

Hi

Also if you want to include switch drop, still test at ceiling rose with light switch on. Use Switch live, Neutral and earth. Then you get longest path of Live.

Malc,

how/why would you use three leads to test R1+R2:confused:
 

Reply to Testing Zs at Lighting switch's with no neutral in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

Hi all, I've been at this all night for a smart switch I've installed for exterior lighting for the house located in the eve's of the house attic...
Replies
0
Views
236
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top